Discuss supply to a shed on a tns system in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
Hi everyone
I have a question I have been asked to look at a job this week and I am a bit puzzled.
A chap I know has a shed connected to His down stairs ring to a garden shed via a 2 core swa cable. Its connected to the rear of a outside socket the armour of the swa is connected to the cpc at the outside socket and in the shed the swa cable armour is connected into the earth terminal in a garage consumer unit that just has 2 mcbs in it no rdc. A 6amp mcb that powers a 2ft led batten and a 20amp mcb that connects to a double socket and then there is a 16mm cpc that connects to a earth rod beside the shed is this acceptiable
It looks a bit naff to me the fact that the tns set up has a earth electrode in it as well
thanks phil
 
Last edited:
TNS with a earth rod are you certain it is a TNS .is metal pipe work in .
The shed needs to be on it own if it has a c/u for the circuits if thats the case .is the circiut that the shed on has any RCD protection .
 
Last edited:
You have effectively described a spur (unfused?) from a ring final circuit supplying two double sockets and a light.
If this is unfused it is not permitted as an unfused spur should only supply a single accessory.
The consumer unit is fairly redundant but the light should be fused down.
However installing a fused spur before the outside socket would resolve most of this.
The addition of an earth rod is probably not really a problem, although in effect it does introduce an earthed conductive part into the shed which might cause potential difference issues, however because it is earthed back to the house CU it should not matter.
Presumably the house ring is 30mA RCD protected and if so this is fine, if not then there are other issues with the house as a whole.
Overall a right old mess.
 
Hi The house is a TNS system and all circuit in the house are RCD protected the house is only a year or so old. The earth rod has been added at a later date when the shed was erected the rcd protection is from the house DB. Also if the shed supply is from a socket and the shed has a lighting circuit and a socket circuit should this be a notifiable job
Phil
 
It is a spur from a ring so not notifiable (unless in Wales as garden power). It would be hard to state you had complied with the building regulations as it does not comply with BS7671.
 
I doubt he got a certificate for the work but from what you describe it ought to be a minor electrical installation works certificate for a spur, but the installation of a consumer unit, even if it is pointless, is theoretically notifiable and would require an electrical installation certificate; the consumer unit is effectively a couple of circuit breakers in a box and not really a consumer unit as it is supplied from a final circuit.
Installing it as a spur there would be test results for the spur (including the RCD tests).
Installing it as a consumer unit would require tests for the "distribution circuit" (i.e. the ring and spur), and tests for the "circuits" in the shed.
Fusing down at the start of the spur from the ring and removing the consumer unit and earth rod and fitting a further 3A FCU for the lights might be a solution.
 

Reply to supply to a shed on a tns system in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello all, Looking for help here as I've come across a strange call-out today. Bare with me here: Got a call from a customer saying they had...
Replies
13
Views
2K
Evening everyone . Currently looking at pricing a job up . It’s a hot tub supply . Outside socket with a few spare ways in an outdoor cu . 10mm...
Replies
7
Views
553
Hi all, I'm planning on adding some lighting to an old stone shed, there's currently a 2.5mm² SWA supply to the shed only supplying one IP rated...
Replies
7
Views
1K
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
As the title says, I am looking for a recommendation for an enclosure and gland arrangement to electrically isolate or divorce the earth/armouring...
Replies
25
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock