Hi Everyone
A company has had its inspection failed for the following reason a Ring final circuit wired in pvc high impact 20mm conduit is not RCD protected. The situation is an accomodation block at a college inside the rooms with access corridoors.
!. The onsite gude states 3.6.1 pagees 21 and 22
(ii) Rcd required for socket outlets in domestic and similar installations
NOTE: Cables installed on the surface do not require Rcd protection
3.6.2 TN conduit installations
where cables in wall or partitions have an earthed metallic covering or are installed in steel conduit or similar 30ma rcd protection is still required in the following circumstances
in this case
circuits with socket outlets not exceeding 20A
They then stated that in the big red book
411.3.3
(rcd to 415.1 30ma taken as read) rcd shall be provided for
i) socket outlets with a rated current of not exceeding 20A that are used by oridnary persons and are intended for general use
Right now here we go
For the onsite guide cables in conduit not metallic are not in the wall but on it
so basic and fault protection are met by the mcb and conduit also mechanical protection.
if these are fullfilled additional protectuion by an rcd would not be needed but to cover all the additional protection by an rcd is an added bit of insurance.
So to get this by going back to the regs it effectively nulls the onsite guidance ??????????
ok we all know the onsite guide is only a guide but if the average sparks works to the onsite guide he falls down falt on intruptaion by an inspector ?
Solution is simple rcbos in the board job done
So should designer ignore the onsite guide and how practically would it affect the day to day installtions sparkie life
comments please
cheers
A company has had its inspection failed for the following reason a Ring final circuit wired in pvc high impact 20mm conduit is not RCD protected. The situation is an accomodation block at a college inside the rooms with access corridoors.
!. The onsite gude states 3.6.1 pagees 21 and 22
(ii) Rcd required for socket outlets in domestic and similar installations
NOTE: Cables installed on the surface do not require Rcd protection
3.6.2 TN conduit installations
where cables in wall or partitions have an earthed metallic covering or are installed in steel conduit or similar 30ma rcd protection is still required in the following circumstances
in this case
circuits with socket outlets not exceeding 20A
They then stated that in the big red book
411.3.3
(rcd to 415.1 30ma taken as read) rcd shall be provided for
i) socket outlets with a rated current of not exceeding 20A that are used by oridnary persons and are intended for general use
Right now here we go
For the onsite guide cables in conduit not metallic are not in the wall but on it
so basic and fault protection are met by the mcb and conduit also mechanical protection.
if these are fullfilled additional protectuion by an rcd would not be needed but to cover all the additional protection by an rcd is an added bit of insurance.
So to get this by going back to the regs it effectively nulls the onsite guidance ??????????
ok we all know the onsite guide is only a guide but if the average sparks works to the onsite guide he falls down falt on intruptaion by an inspector ?
Solution is simple rcbos in the board job done
So should designer ignore the onsite guide and how practically would it affect the day to day installtions sparkie life
comments please
cheers