Discuss SWA Fly lead in the Industrial Electricians' Talk area at ElectriciansForums.net

ive always put half the size in on every swa ive terminated,,,,or if there is a seperate cpc run with swa i take into panel through a stuffing gland up to earth bar..
 
What about when its a main panel , we have a job with the swa cables to be terminated into the galvanised steel glandplate on the top of the panel , this is already bolted to the chassis of the panel and has a 16mm bond from the top plate to the earth bar. The panel is a schneider okken . Would you take a flying earth lead from every SWA banjo to the bar in a CPC half the phase size ?? or would this just be overkill. They are using the armour as the CPC for all these outgoing circuits so best readings are needed to meet the disconnection times .

any oppionions welcomed
 
When i worked in a factory i would make off the swa as normal then run a 6mm
earth cable from the brass lockring to a earth clamp on the armour.
contractors used to say it was overkll but it maintains the earth if the
gland comes loose.
 
Pblec I mean this with no dis-respect but I hope you are not undertaking this task as the main installer as you could be a little out of your depth. We are willing to help you on here but basic understanding of earthily and bonding is a must.
 
no disrespect i know what it is thats why i asked

main protective bonding conductor - earth wire comeing into house

main equipotential bonding - incoming services, steel etc

supplementory bonding - is additional bonding

wp says its earthing and not supplementory bonding i beleive earthing and bonding are the same thing and was hopping for him to clarify
 
Well for staters the earth coming into your house is called your MAIN EARTHING CONDUCTOR not bonding.
And secondly wp is right what your proposing is an earth tag. Your earthing the SWA armour.
Bonding is bringing all extrenous parts to the same potential so different potentials don't exist.
 
S = Isquared x T then hit square root and finally divided by K i think lol cant show exactly asdont know how to on the laptop its in the regs pg128
S = is the nominal cross sectional area of the conducter
I squared is the value in amperes of fault current of negligable impedence which can flow through the protective device , due account being taken fof the current limiting effect on the circuit impedences and the limiting capability I2t
T the operating time of the disconnecting device in seconds corresponds to the fault current I amperes
K is the factor taking into account of the resistivity ,temperature coefficient and heat capacity of the conductor material , and the apropriate initial and final temperatures
 
simon please its too easy check out page 167 544.1 amendment 1 2011

is supplementory bonding not connecting of conductive parts of electrical and non electrical items to prevent a dangerous voltage to prevent a dangerous voltage apearing between them under an earth fault conditions
 

Reply to SWA Fly lead in the Industrial Electricians' Talk area at ElectriciansForums.net

Similar Threads

RCBO fly neutral lead what should I be using and what supplier has them Pict
Replies
8
Views
292
resitting Saturday my am2 4 sections a3/b/d/e swa and sy failed on protective conductors on both swa i under stand thats the earths i...
Replies
1
Views
1K
Hello everyone, Following on from my previous post where I received advice on taking a spur off a 40a feed (thank you). I performed the work...
Replies
4
Views
857
If cpc core is present i.e. it's either 5 core three phase or 3 core single phase — is a banjo connected with a brass screw into steel trunking...
Replies
7
Views
1K
Hi, I have always used banjos when earthing the armour on an SWA but have now switched to earthing nuts. I am making off a 10mm fly lead to the...
Replies
17
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock