Not in an Electrician's mind it doesn't, just checked your profile, those qualifications you have, are designed for practising Electricians, designed to update their knowledge. These courses do not make you an Electrician, if you were told that by the Training Schools then you have been duped.Give a guy a break. If you looked at my profile you would see I'm a qualified electrician but still very new to the trade. I thought this forum was here to help people like me who are still learning, rather than knock us down. If people can't be open and ask questions that might show they are inexperienced then it rather limits the usefulness of such forums. I'm already aware I lack practical experience and have been trying to find someone with more experience I can work with as an Electricians Mate to remedy that. In the meantime I turn to you guys... As it happens I probably am going to involve someone with more experience on this one, as no answers from anyone on the routing question, although I appreciate that's difficult to visualise on a forum such as this.
CSA may be obvious when you have been in the industry for years, but when you see a listing for 25mm SWA that specifies 25mm OD and makes no reference to CSA/core size alongside, it does raise a question mark in one's mind.
DeletedDon't take offence @Msitekkie . By most of the opinions on here I'm neither an 'electrician' or 'engineer'.... Everyone to their own....
House+garage+workshop:You’re probably getting the calculations wrong then, the average house doesn’t need much more than about 20A.
Out of interest how did you arrive at a figure over 100A for a house?
He was the one that brought up qualification defining his status in fairnessDon't take offence @Msitekkie . By most of the opinions on here I'm neither an 'electrician' or 'engineer'.... Everyone to their own....
House+garage+workshop:
Starting with 7.4Kw Induction Hob (1st 10A plus 30% of the remainder) 16.6A already...
3Kw Immersion heater - No Diversity allowed another 13A...
3Ring + 3 Radial Circuits (100% of 1st & 40% of rest) 32+49.6 = 81.6A
+ 4 x 6A lighting - haven't worked out all the lights I'm having yet, so lighting diversity still up in the air (although mostly a mix of compact flourescents & LEDs).
I know diversity is a bit of a black art so any constructive comments/suggestions welcomed. As the immersion is only used in emergencies if CH not working. I'm wondering if there are any options there.
P.S I don't have a clamp meter yet.
as no answers from anyone on the routing question, although I appreciate that's difficult to visualise on a forum such as this.
Radials are sockets in Garage, workshop & new utility room. Upstairs & downstairs are existing rings - don't really want to add work by converting to radials if I can avoid. Splitting kitchen off downstairs ring onto its own.There’s little chance those ring circuits are going to pull over 80 amps after diversity, why not have a 20a radial upstairs, 20a radial downstairs and a ring for kitchen?
What are other radial circuits,
Think of peak times morning evenings when most load will be consumed should only be short periods when applying diversity,
a bs88-3 (new bs number for 1361) will take 190a for half hour fig 3A1 bs1761
I doubt very much your ever going to come anywhere near this.
I would recalculate put in an 80a kmf
House+garage+workshop:
Starting with 7.4Kw Induction Hob (1st 10A plus 30% of the remainder) 16.6A already...
3Kw Immersion heater - No Diversity allowed another 13A...
3Ring + 3 Radial Circuits (100% of 1st & 40% of rest) 32+49.6 = 81.6A
+ 4 x 6A lighting - haven't worked out all the lights I'm having yet, so lighting diversity still up in the air (although mostly a mix of compact flourescents & LEDs).
I know diversity is a bit of a black art so any constructive comments/suggestions welcomed. As the immersion is only used in emergencies if CH not working. I'm wondering if there are any options there.
P.S I don't have a clamp meter yet.
Reply to SWA For meter tails? in the UK Electrical Forum area at ElectriciansForums.net