an outbuilding is supplied by a 50mm twin SWA cable from a PME supply

The assessor has told me to convert to a TT as the steel csa is too small, is there a way I can prove that surely a 50mm twin swa sheath is suitable to be a 16mm earth?
 
an outbuilding is supplied by a 50mm twin SWA cable from a PME supply

The assessor has told me to convert to a TT as the steel csa is too small, is there a way I can prove that surely a 50mm twin swa sheath is suitable to be a 16mm earth?
yes look at this table
SWA
 
Sorry never copied, there is a table you can refer to unfortunately I can't copy it, try again
file:///C:/Users/Pete/Desktop/Resources/SWA%20CPC.pdf
No no
an outbuilding is supplied by a 50mm twin SWA cable from a PME supply

The assessor has told me to convert to a TT as the steel csa is too small, is there a way I can prove that surely a 50mm twin swa sheath is suitable to be a 16mm earth?
Has it worked this time
file:///C:/Users/Pete/Desktop/Resources/swa-as-the-cpc.html
 
Sorry never copied, there is a table you can refer to unfortunately I can't copy it, try again
file:///C:/Users/Pete/Desktop/Resources/SWA%20CPC.pdf

Try the 'Upload a File' option near 'Post Reply' button mate.. That might work
 
Try the 'Upload a File' option near 'Post Reply' button mate.. That might work
an outbuilding is supplied by a 50mm twin SWA cable from a PME supply

The assessor has told me to convert to a TT as the steel csa is too small, is there a way I can prove that surely a 50mm twin swa sheath is suitable to be a 16mm earth?
Chris sorry can't copy and paste my table try Google SWA as the cpc should come up with some thing.
 
Hi - looking in GN8 tables B 1, 2 or 3 it has 50mm swa with steel of 68 (2 core), 78 (3 core) or 90 (4 core). For bonding it's the ratio of resistivity which is about 8. This means the steel armour is worth about 8.5, 9.75 or 11.25 mm2 of copper. The incoming DNO neutral may be bigger than 50, but even 50 needs 16mm (Table 54.8).
 
Keeps me entertained every few weeks theres just like 3 posts from pete with links to a file on his desktop that nobody can obviously access then he eventually figures it out..... Then forgets for next time :D

Leave him alone...you may need to know how to replenish a Le Clanche Jar,one day,and he'll not help you...;)
 

Reply to Swa sheath size too small in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
As the title says, I am looking for a recommendation for an enclosure and gland arrangement to electrically isolate or divorce the earth/armouring...
Replies
25
Views
5K
Hi everyone, A diversity question concerning 2 consumer units fed from 100amp DNO supply Background, So I have an 18th Ed compliant consumer...
Replies
9
Views
2K
Been looking at a CU change in a small office and would appreciate comments on the following. Office is supplied from the mains intake in the...
Replies
52
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock