hi guys. got a job to quote for for for an outbuilding. in the past been lucky enough to get an swa cable under the ground, but this time theres not much chance of that.
as its for only a couple of sockets my easiest and cheapest route would be to fuse down a spur from the ring inside the conservatory going thorough the wall into a adaptable box with twin and earth,from there to swa under a couple of flags to the fence. now this is where it gets a bit akward. its a concrete fence and its landscaped about 20 foot to the summerhouse.no chance at all of getting underneath, is it acceptable to clip the swa to the fence and keep it on the surface,bearing in mind that there is a load of bushes and trees what will be in front of this cable so not really accessable or visable. whole house protected with 17th edition board and its a tn-s.would just like to hear your thoughts on this...
many thanks daz...
 
there is absolutely no reason at all why you can't cleat the SWA on the surface of the fence. some might say it's better than being buried, as you can see it.
 
As telectrix says Cleating the SWA is OK as it is visible and the SWA provides mechanical protection. As an alternative why not clip some PVC conduit to the fence posts and push the SWA down that, quick easy and neat
 
I had a similar problem recently with needing to put a 70m run of 25mm/3 SWA down to a garden workshop - was reluctant to just lob it on the ground in the border as figured it would be semi-buried by autumn, but the fence/boundary wasn't up to the job of cleating a cable that heavy. Solution was to give the customer a diagram of a little mini fence that they could build in 3x4, about 18" off the ground to cleat to instead. As a bonus, they got a way of keeping their kids football out of the roses!
 
Depending on the construction of that concrete fence, you may find it a little more troublesome than you think. If it's these precast concrete fence's you may find that it's made up of more steelwork than you think and the concrete make-up has more stone pebbles than it does sand and cement mixture. Great chunks may slit out of this stuff trying to get a fixing into it. Other than that, as others have said .. no problem cleating direct to the fence!!!
 
thanks malcolm. when i go back to survey the garden again i was going to double check that it was a ring and not spurred before giving them a final price. but a very well brought up point. what a great forum.
many thanks daz...
 

Reply to swa to outbuilding in the Australia area at ElectriciansForums.net

Similar Threads

So I have a job of installing an old cast iron lampost which will need to be buried into the ground about 600mm deep due to its weight. I am...
Replies
11
Views
2K
Hi, I have just been to a job today to provide power to an outbuilding, 75 meters down the garden. The supply is PME, I plan on splitting the...
Replies
20
Views
2K
J
Hi all, I'm having some trouble designing an installation for an outbuilding. It's about 110m from the nearest CU in the house, which is fed via...
Replies
14
Views
2K
JRave
J
S
Hi folks, Rural domestic property with 2 outbuildings. TN-C-S with additional earth rod (believe was upgraded to underground TN-C-S feed from...
Replies
11
Views
6K
SW1970
S
M
Been asked to do a quote for an outbuilding.Outbuilding needs a shower (for dog grooming/washing) , sockets and light. What i intend to do is run...
Replies
3
Views
2K
pushrod
P

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock