I've been doing a PIR today and to my horror and surprise I discovered that the only device, between the 60 Amp main distributors fuse and the pool pump was a 30A 10mA RCD (if you ignore the henley block, the 16mm tails! and the SWA)
View attachment 2615
Looks like some remedial work is coming up!
Given that the SWA is connected directly to the metal casing, and the RCD shown is the only one in the house is the best solution to remove the existing RCD and fit a 2 way metal consumer unit with a RCD and 16A MCB? Also would it be best practice to upgrade the tails too?
Comments please!