Discuss Switched FCU with LED indicator in the DIY Electrical Advice area at ElectriciansForums.net

Reaction score
1
Hello all,

Im looking advice. I'm a diy'er. I have just replaced an old double socket and switched fcu with new stainless steel ones. My previous fcu would have the neon light lit, when switched on. My new one has the led lit when either switched on or off. It's lap brand from the screw fix.

Have i wired it wrong for it to be always on?

Also after fitting I replaced the fuse in the consumer unit. And noted the rcd had flicked off. I put it back on and all is working.

Should the rcd have tripped?

Thanks in advance for replies
 
Hi John,

Welcome to the forums.

It sounds like you have the supply to the SFCU connected to the load terminals (as this is where the indicator will be connected to).

As for the RCD tripping, this can sometimes happen when (whilst cutting a cable for example) you momentarily join the neutral and earth conductors.
 
Hi John,

Welcome to the forums.

It sounds like you have the supply to the SFCU connected to the load terminals (as this is where the indicator will be connected to).

As for the RCD tripping, this can sometimes happen when (whilst cutting a cable for example) you momentarily join the neutral and earth conductors.
Ok thanks for that. I guess I chose wrong when choosing which cable was the supply and the appliance. I shall swap them about tomorrow.
 

Reply to Switched FCU with LED indicator in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi guys, newbie posting! Does the following sound ok... Existing circuit: SOCKET on a ring -> spur to SWITCHED 3A FCU -> SWITCH -> hardwired FAN...
Replies
11
Views
631
our dimmer switch stopped working after 7 years so went to replace it at the weekend. When I opened it up, the black wire was in the common slot...
Replies
0
Views
186
I installed an illuminated switch (switch is lit when circuit is off) for my porch light. I noticed that even when off, my LED porch lite is...
Replies
6
Views
1K
Hi all I've been changing the halogen downlighters in my house to LED's. I have three rooms that use dimmers, two of them have two switches each...
Replies
0
Views
361
Today I went to fix a minor loose screw on something and after switching off, etc, got out my Martindale VT12 continuity & voltage tester and...
Replies
3
Views
419

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock