This question is purely out of interest, I'm a substation apprentice while we do some LV installation work its not much and no design work fitting only.

But today I've been helping a sparkie friend do some work(just attaching conduit to wall no actually wiring) for local community group.

So the question why is the neutral to the DB from a switched fuse isolated (if that the right term) not switched but at the DB it's self does switch neutrals?
 
Generally neither a switch fuse nor a DB will have switching of the neutral in a TP installation unless it is is a non TN system or a special type of installation.

Most TP DBs will have a triple pole main switch with a test/disconnect link for the neutral which requires the use of a tool.
 
Would there be anything wrong with having the neutral switched, should also mention it's 3 phase board?


If the neutral is to be switched then it should ideally be by a last break/first make contact to prevent the lives being connected before the neutral.
If the neutral contact of the switch were to fail for any reason you could end up with the installation having a floating neutral which can be dangerous.

In an installation where the neutral is reliably connected to earth (TN system) there is no need to isolate the neutral and so the risk of a failed switch contact can be avoided by nit switching the neutral.

In other installations where the neutral can have a voltage between it and earth it needs to be isolated to achy eve a proper isolation and so it must be switched.
 

Reply to Switched Neutrals or not in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi there, Any advice on this would be greatly appreciated! (Note, this is not a DIY, I'm using a fully qualified electrician, just posting here...
Replies
8
Views
591
Howdy DIY soldiers, first post here. My question comes down to whether it would be particularly unsafe for me to temporarily wire nut and tape a...
Replies
2
Views
1K
I'll start by saying - I have absolutely no intention of doing any wiring or anything electrical myself. You get someone professional to do a...
Replies
8
Views
743
Hi All, thanks in advance for any guidance you can provide. I will of course turn off everyhing at the consumer unit before doing anything. I...
Replies
0
Views
426
Has anyone here got experience of doing a soil / earth resistance survey for the design of a large-ish site? We might be looking at a fenced area...
Replies
1
Views
392

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock