Cj24

Hi cud u help, I was just wondering when you have for instance a 3phase isoltor it's classed as a 3pole sw am I right as in it sw's the 3 phases but why do u not sw the N therefore it being a 4 pole sw and y do we not sw the N and in other isolators we do sw the N
 
Hi cud u help, I was just wondering when you have for instance a 3phase isoltor it's classed as a 3pole sw am I right as in it sw's the 3 phases but why do u not sw the N therefore it being a 4 pole sw and y do we not sw the N and in other isolators we do sw the N

In a TT installation you would have to break all live conductors or where they can't be regarded as having a sufficiently low impedance to earth.
 
Last edited:
Like I said in TN systems the neutral is reliably connected to earth.

Therefore in TT all live conductors must be broken. In TN all line (phase) conductors must be broken.
 

Reply to Switching poles in the Canada area at ElectriciansForums.net

Similar Threads

Hello everyone, I’m based in the ROI and live in a rural location. Yesterday evening my electricity supply started to switch on and off randomly...
Replies
2
Views
2K
Hi folks, I'd like to get my Nest thermostat up and running with the gas combi boiler (Worcester Greenstar HIghflow 440 Standalone). FYI - I...
Replies
9
Views
1K
I don't "do" solar, but I've been asked to comment on an aspect of a new domestic solar installation by others. There is no overload or fault...
Replies
7
Views
1K
Hi all, Just to be clear, I'm not looking for advice on upgrading but rather just clarification of our existing setup. We need to upgrade the...
Replies
12
Views
1K
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
754

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock