Discuss Switching in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Mark.W

-
Reaction score
31
Evening Chaps

I've got a switching conundrum that I was hoping one of you guys could help me with!

I've been working on a heating system and the previous spark managed to run 2 pumps either together or independently with one boiler and a 2 channel programmer!

I however cannot get pump 1 to run without pump 2 also running, because they have a common live at the boiler??
I've tried everything and had to resort to using a NC contactor to stop pump 1 from running when pump 2 was running, but the previous spark never used a contactor.

I hope that made sense, if you need any further info just give me a shout!

Thanks for your help!
Mark
 
Hi Mark,

What type of heating system is it and what is the job that each of the pumps are carrying out within the heating system?
 
Hi

It isn't any type of system, basically all there was, was 2 pumps and no valves. 1 of the pumps controlled upstairs heating and the hot water and the other pump controlled downstairs heating. There was one room stat on downstairs pump and that was it no stat for upstairs heating and also no cylinder stat, the cylinder stat apparently got taken out recently when the customer had solar thermal installed!

Very bad I know!!
 
isit an old system.? sounds like the downstairs pump should be wired off the roomstat hest rise terminal.! but what is controlling HW and up rads.? not just the programmer i hope, if no cyl stat whats stopping cyl acting like a big kettle.? hope its a vented cyl.?
 
We've just turned upstairs circuit into an S plan by putting valves in for HW and HTG! Left downstairs as it was, on its own pump and controlled via the room stat! We've also installed a new upstairs room stat and cylinder stat, which yes as you thought, was fed directly from the programmer!
 
sounds like you done a good and very needed upgrade to this system.! if you wire your pumps from the motorised valve rather than from the boiler you can eliminate the shared pump live at the boiler.!
 
Well it sounds to me like an old gravity hot water system with pumped central heating and as an effort at controlling it they have bodged it up a bit. The only way that I can see it would have worked is that the prog was configured as a time switch where you can have the HW side on independantly but the CH side would only work if the HW was calling.

Wired from the HW side of the prog would be the upstairs pump for CH and the HW circuit and the boiler.

Wired from the CH side of the prog would be the downstairs pump for the CH and nothing else, so you could not have the downstairs CH on unless the upstairs CH and the HW is calling at the clock.

This is the only way that I can think of to have the pumps working independantly.

Very old school.
 
sounds like you done a good and very needed upgrade to this system.! if you wire your pumps from the motorised valve rather than from the boiler you can eliminate the shared pump live at the boiler.!

Both pumps will be common with the boiler switch live so they will both work which ever is calling, got to be careful that you don't have a pump trying to push water up 2 closed valves on the new s-plan part
 
That's the problem and to counteract that I have installed a NC contactor between P1 and the boiler so that when pump 2 runs pump one is disconnected, the coil is energised by the room stat calling for heat! But how did the previous spark manage to run both pump independently?? That's what has got me baffled! They were both run to the boiler....???
 
It worked that when they pressed central heating advance pump 2 would run and when they pressed hot water advance pump 1 would run. Both wired back to the boiler.... Strange!!!!
 
What happens when need both pumps running , one after other... I used relay in similar situation before. But running pump from valve seems good
 
It worked that when they pressed central heating advance pump 2 would run and when they pressed hot water advance pump 1 would run. Both wired back to the boiler.... Strange!!!!

It seems that the HW and boiler worked on gravity and the prog just controlled the pumps in essence and that HW advance controlled pump 1, gravity HW and boiler.
 
The problem is only one pump has valves, like an S Plan, but we haves third channel which is a pump controlled via a room stat with no valves!
 
When you need to run both pumps then both pumps will run! There are 3 channels, 1 is HW, 2 is upstairs heating, 3 is downstairs heating! If I only want downstairs heating on (pump 2), then it goes from programmer to room stat to NC contactor A1 and from room stat to P2 then boiler, A2 on the contactor is connected to N, we then have P1 in 1 terminal and boiler in the other! So pump 2 runs with pump 1 off, ( the stat calling for heat energises the coil and opens the contact). If we then also want to switch upstairs heating on, we hit Channel 2 heating, which runs from programmer to upstairs room stat, to the 2 port valve, then on to pump 1. (Boiler is already running) The same for HW

It's late and I hope that makes sense!
 

Reply to Switching in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

1 - Major supply fault, details unknown. By time I get there DNO already put in genny and are digging up road. 2 - Reason for call, heating not...
Replies
4
Views
586
I've always thought I was quite good a wiring heating systems, I can do Y plan, S plan, UFH set ups, "normal" thermal stores etc, you name it and...
Replies
4
Views
904
  • Article
Do you install new heating systems? Ever had a missing cable run between a boiler and a pump? Using MAINSLINK - the pump overrun solution - you...
Replies
0
Views
692
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K
Hi everyone I've moved into a flat and I've decided to replace the original electric switches and sockets with white ones. I've done them all...
Replies
3
Views
785

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock