  1. brav
    Offline

    brav Solar Guru

    Iv just been to look at a job in a cafe, the customer needs a cooker circuit and a radial adding the the installation, the 3 phase D-board is in the same room as where the two extra circuits will be.

    All the circuits tht are already in this room, radial for boiler and radial sockets feeding fridges/freezers are pvc/pvc Twin&E in 25x16mm minitrunking.

    The customer wants the two circuits i have to add in mini trunking, but im i allowed to use twin and earth in mini trunking and what Reference Method would tht apply to?

    thks guys
     
  2. 1shortcircuit
    Offline

    1shortcircuit Guest

    Why would you not be allowed?

    Providing you adjust your cable calcs accordingly then you will be fine.

    Reference Methods can be found in the On-Site guide;) :thumbsup
     
  3. Farmelectrics
    Offline

    Farmelectrics Farmelectrics Electrician's Arms

    Location:
    Wirral
    Business Name:
    Farm electrics
    Yes nothing wrong with mini trunking not everyone's cup of tea but sounds the right choice for you
     
  4. Paul.M
    Offline

    Paul.M Trusted Advisor

    Location:
    Lost in Space
    Mini trunking has been omitted from the 17th, just use conduit method for calcs.
     
  5. netblindpaul
    Offline

    netblindpaul Trusted Advisor

    Location:
    South Wales
    Why put T&E in MT?
    Just use singles easier to install.
     
  6. Adam W
    Offline

    Adam W Electrician's Arms

    Location:
    Bournemouth
    That's debatable. T&E is cheaper, and you only get left with 1 part roll to use up, not 3.
     
  7. netblindpaul
    Offline

    netblindpaul Trusted Advisor

    Location:
    South Wales
    That depends on what you use, my T&E sits on the shelf for much longer than my singles!
     
  8. telectrix
    Offline

    telectrix Scouser and Proud of It Trusted Advisor

    Top Poster Of Month

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    it will if you do mostly industrial , but if 90% of your workm is domestic, then it's the singles that will become home for the spiders.
     
  9. Top Cat
    Offline

    Top Cat Electrician's Arms

    Location:
    Gloucester
    Well i didn't know that, learn something new every day. Must spend more of my waking hours studying the BGB!
     
  10. JUD
    Offline

    JUD Electrician's Arms

    Location:
    East Yorkshire
    Still there in my BGB (Table 4A2 from page 317) although it's defined as "cable trunking".
     
  11. netblindpaul
    Offline

    netblindpaul Trusted Advisor

    Location:
    South Wales
    Tel,
    Over 90% of my domestic work is in MT, however, I concede that it is a small percentage of my total work.
    But I feel that for what I do it is more cost effective to use singles, no sleeving, no stripping of sheath, easier to run in, lighter to handle the drums, more flexible, I HATE solid conductors with a passion! ;)
     
  12. brav
    Offline

    brav Solar Guru



    Which number were u looking at on page 317 mate? Number 8/9 Multicore cable in a cable trunking on wooden or masonary wall?

    I was lead to believe Multicore Cable non-armoured they are talking about there, is the type used for extension leads etc, not Flat pvc/pvc twin and earth?

    Also tht has a Reference Number 'B', table 4D5 doesnt have Ref Number 'B' as a choice? thks.
     
    Last edited: Jun 7, 2012
  13. JUD
    Offline

    JUD Electrician's Arms

    Location:
    East Yorkshire
    Table 4D2A (page 334). Multicore 70°C thermoplastic insulated and sheathed cables.

    Reference Method B (enclosed in conduit on a wall or in trunking etc.​)
     
  14. telectrix
    Offline

    telectrix Scouser and Proud of It Trusted Advisor

    Top Poster Of Month

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix

    so do i. would much rather work with conduit, trunking etc. than with T/E. unfortunately. in the present economic climate, you have to grab what work there is, and in my situation, most of that is domestic. YUK.
     
  15. Paul.M
    Offline

    Paul.M Trusted Advisor

    Location:
    Lost in Space
    Agree with you Jud but in another page it says that mini trunking is still under review as a method? Clear as mud yet again.

    Me and Tel had a debate about this a couple of months ago I think.
     
Loading...
Similar Threads - mini trunking Forum Date
Understanding minimum CPC requirements? Electrical Forum Sep 16, 2018
Me in a nutshell (with minimum of 20 characters) New Member Introductions Aug 15, 2018
Thread Status:
Not open for further replies.

Share This Page

Users found this page by searching for:

  1. ref method trunking

    ,
  2. how to discuss cable trunking method

Electricians Directory Post a Domestic Job Post a Commercial Job