right I get a bit confused with working out the Tabulated values (I am training and have exams tomorrow for Initial verification) on the Ze and Zs anyone on here what to explain how this works on the earth loop impedance, please can someone explain what I am overlooking ?thanks, Jules I understand he Equation Zs =Ze+ (R1+R2 ) but I not getting the answer I want I must be overlooking something
 
It might be worth joining the Trainee forum if you're on a current course.
 
I am not quite sure what you are referring to on working out the tabulated values as the tabulated values do not need working out as they are in the table.
To calculate the Zs required without using the tables you use the formula Zs max = Uo * Cmin/ Ia.
U0 is 230 Vac for single or three phase general supplies.
Ia is the current to operate the protective device in the time required (e.g 0.4 s for a final circuit <32 A (63 A with sockets)operating at the above U0).
Cmin is given as 0.95, to account for drops in the supply voltage.

So for a B32 circuit breaker to BSEN60898:
Type B operates by magnetic trip (i.e. almost instantly) at between 3 and 5 times rated current. For 32A the worst case would be 160A (5*32).
Zs = (230 *0.95)/160 = 1.37Ω as given in BS7671.

The tables for the maximum values of Zs permitted for the protective device in use:
The tables in BS7671 are giving the maximum resistance permitted when the live conductors are at their normal operating temperature (generally 70°C for most situations).
The tables in the on site guide are corrected for the fact that when actually measuring resistance the conductors are more likely to be at ambient temperature, so the values are given for 10°C which is applying a correction of 0.8 times the BS7671 tabulated value because the resistance will rise as the conductors heat up.

This means that when you are measuring Ze and R1+R2 in practice and you want to compare your results with the values given in BS7671 you should either multiply your result by 1.25 or multiply the BS7671 values by 0.8 to see if the measurement is compliant.

e.g. You have measured a Ze of 0.3Ω and an R1+R2 of 1.0Ω and your are using a 32A type B circuit breaker.
Your calculation Zs= Ze+(R1+R2) gives 1.3Ω
If you compare 1.3Ω to the BS7671 tabulated limit of 1.37Ω you may think this is compliant.
However if you multiply your result by 1.25 to give you the expected resistance when the conductors are at 70°C you get a Zs of 1.625Ω which is non compliant.
If you look in the on site guide the tabulated (corrected) value is 1.1Ω which is lower than your measured 1.3Ω so the circuit is non compliant.
 
Not sure what you are asking. Are you asking what the difference is between Zs and Ze?

Only things you should need to know for initial verification is, what they both mean, how to calculate and measire both and how to compare results with the values. Also need to know the difference between tabulated values and the rule of thumb (x0.8)
 

Reply to tabulated values of Ze and Zs in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Evening everyone, I was taught when carrying out Zs testing to test both L-PE and L-N and record the highest result of the two tests for my Zs...
Replies
11
Views
2K
Hi all , The measured value of loop impedance for a circuit is 2.4Ω. If the temperature at the time of the test was 20°C and the cable is 70°C...
Replies
4
Views
702
So I’m doing my level 3 design project at the moment, and I’m on the question where you do all the calculations on each circuit, I’ve taken the...
Replies
3
Views
1K
Got my am2 coming up on Tuesday and I know I have to calculate my Zs readings Maybe I’m overthinking this but am not sure if I need to use the Ze...
Replies
17
Views
3K
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock