Discuss Tail sizes from PV sub-board in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

To prevent the chances nuisance tripping the main board.
If you are worried your new install is likely to cause nuisance tripping then you need to reassess what you are doing as the best method is to install directly to the existing dist board providing there are spare ways.
 
If you are worried your new install is likely to cause nuisance tripping then you need to reassess what you are doing as the best method is to install directly to the existing dist board providing there are spare ways.
I wouldnt say it’s the best way if there is spare way on a RCD protected way that shares the same side as a socket circuit for example. It would actually be non compliant due to how long the inverter takes to shut down which can be up to 5 seconds under G83.
 
If you are worried your new install is likely to cause nuisance tripping then you need to reassess what you are doing as the best method is to install directly to the existing dist board providing there are spare ways.

That's VERY wrong for the reason Lee gave above ........... but is the most common method of install I see ......
 
I wouldnt say it’s the best way if there is spare way on a RCD protected way that shares the same side as a socket circuit for example. It would actually be non compliant due to how long the inverter takes to shut down which can be up to 5 seconds under G83.
Where does it state this would be non compliant, not had much to do with these systems so would be interested.
 
I wouldnt say it’s the best way if there is spare way on a RCD protected way that shares the same side as a socket circuit for example. It would actually be non compliant due to how long the inverter takes to shut down which can be up to 5 seconds under G83.
Learning every day.
If I've understood correctly - in a dual RCD board if they've attached PV invertor to MCB under one of the RCDs, if that RCD detects a fault and trips, great. But the invertor continues to put 230V onto the common MCB busbar. So ADS has not been achieved (!!!).
 
Last edited:
Where does it state this would be non compliant, not had much to do with these systems so would be interested.

I can’t give a regulation, but plain old common sense should be enough.
If a person receives a shock the RCD will trip, but the PV will continue to supply power to all circuits supplied by that RCD for a period of time, therefore defeating the purpose of the RCD and killing the person.
 
Regulation 712.411.3.2.1.1 states that on the ac side the pv cable shall be connected to the supply side of a OCPD for automatic disconnection of circuits supplying current carrying equipment
 
Nuisance tripping "might" be a problem when sharing an RCD, but that's the least of the potential issues. More likely (when using transformerless inverters) is that the Type-AC RCD (usually fitted in residential CUs) might become saturated and never trip under fault conditions. That's in addition to the scenario outlined by others relating to the shutdown times of PV inverters and ADS intention of the primary RCD in the first place.....amazing that this topic still causes discussion so many years down the line!! As for the OP's original question, using 10mm2 tails from henley blocks broken into the meter tails (25mm2) is perfectly fine so long as the OCPD on the PV connection is suitably rated. In fact, I'd go so far as to say this is a better method that using a spare way on the non-RCD protected side of the main CU (various reasons including ease of monitoring and avoiding potential issues with RCDs....)

Just my tuppence...
 

Reply to Tail sizes from PV sub-board in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

hi thank you for help in advance have a potential pv installation for a garage roof that is some 60m from the main house (main incomer in the...
Replies
9
Views
2K
Hi all. I have been asked to take over a job an electrician has started, and has moved abroad. The house is a big mansion, with a 3PH supply...
Replies
49
Views
4K
Quick question. I want to put an isolating 2p switch on my incoming supply from the meter to the board. I want this to allow easier board changes...
Replies
8
Views
778
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
770
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock