Posting a message to the forum will remove the above advertisement
  1. This site uses cookies. By continuing to use this site, you are agreeing to our use of cookies. Learn More.

Discuss Take it or leave it in the Electrical Wiring, Theories and Regulations area at ElectrciansForums.co.uk.

Thread Status:
Not open for further replies.
Please make sure you checkout our forum sponsors, many do discounts for members and, they keep the forum free to use.
  1. Bubblecraft
    Offline

    Bubblecraft Electrician's Arms

    Location:
    Erskine
    Within the past month I've had 2 customers who were wanting a shower swap, like for like. Both have been 9.5kw but have 6mm2 cable instead of 10mm2. Both customers were advised of the dangers & consequences of having 6mm2 on a 9.5kw such as volt drop, ambient temp's, grouping, and thermal insulation factors, and more so, probably the reason why there old one is defunct.

    Both did not want to upgrade their cable so I've said that I would not carry out the work. If I take on the swap, it's me that's got to answer why their new shower is knackered in no time or worse, chance of fire.

    What would you guys have done?
     
    Last edited: Feb 26, 2012
  2. telectrix
    Offline

    telectrix Scouser and Proud of It Respected Member

    Top Poster Of Month

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    check cable run . if it's installed method c then swap shower. leave on 6mm with 32A MCB.
     
  3. Bubblecraft
    Offline

    Bubblecraft Electrician's Arms

    Location:
    Erskine
    Both houses were 15+m from CU though
     
  4. telectrix
    Offline

    telectrix Scouser and Proud of It Respected Member

    Top Poster Of Month

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    around 4.8V volt drop off top of head. acceptable.
     
  5. Bubblecraft
    Offline

    Bubblecraft Electrician's Arms

    Location:
    Erskine
    Forgot to say, it's method A also which if I'm right is 32a, I could be wrong though
     
    Last edited: Feb 26, 2012
  6. telectrix
    Offline

    telectrix Scouser and Proud of It Respected Member

    Top Poster Of Month

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    method A as in thermally insulated wall? or is it in masonry?
     
  7. Bubblecraft
    Offline

    Bubblecraft Electrician's Arms

    Location:
    Erskine
    Masonry mate, sorry
     
    Last edited: Feb 26, 2012
  8. telectrix
    Offline

    telectrix Scouser and Proud of It Respected Member

    Top Poster Of Month

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    not insulated so i would say method C, or possibly method B , 38A
     
    Last edited: Feb 26, 2012
  9. spinlondon
    Online

    spinlondon Forum Mentor

    Location:
    Harlow Essex
    By rights, if the load is 45A/50A, the CCC of the cable is 38A and you protect the circuit with a 32A MCB, then whilst not complying with the Regulations, it should be safe.
    I would imagine that there will be a lot of nuisance tripping, but that would not be your problem.
    Note it as a departure on the Certificate.
     
  10. Bubblecraft
    Offline

    Bubblecraft Electrician's Arms

    Location:
    Erskine
    I'm confused. Please correct me if I'm wrong but isn't method c clipped direct & these are in sold brick walls behind the tiles?
     
  11. Bubblecraft
    Offline

    Bubblecraft Electrician's Arms

    Location:
    Erskine
    But I know what'll happen, after a few trips, they'll be on the blower saying "You couldn't have fitted it correctly. Our old one didn't do it"

    I know this would be the way to do it safely but would you do it & put up with the grief from the customer about a tripping shower?
     
  12. telectrix
    Offline

    telectrix Scouser and Proud of It Respected Member

    Top Poster Of Month

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    agreed. i estimate the load as 39.5A max. assuming manufacturers claim of 9.5kW is not eggagerated ( as is usual). have seen 9.5kW happily running on a BS3871 30A with no problems.
     
  13. tony mc
    Offline

    tony mc Electrician's Arms

    If you look up ref method c it makes mention of masonary brickwork concrete & plaster!
     
  14. Bubblecraft
    Offline

    Bubblecraft Electrician's Arms

    Location:
    Erskine
    Either way, I've not took both on so I know I can sleep at night. For the cost of changing it over, I personally don't think it's worth the grief!
     
  15. telectrix
    Offline

    telectrix Scouser and Proud of It Respected Member

    Top Poster Of Month

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    BS7671 does not have a reference method for T/E in masonry walls. a boffin at the IET told me last year that ref.B would be the closest
     
Loading...
Similar Threads - leave Forum Date
Domestic Leave existing ceiling rose within new metal light fitting?? Electrical Forum Tuesday at 1:54 PM
Commercial Use of 16a 230v ip44 plugs & sockets outside laying on wet grass / leaves Electrical Forum Dec 3, 2018
Thread Status:
Not open for further replies.

Share This Page

Electricians Directory Post a Domestic Job Post a Commercial Job