My understanding, is that installations which complied at the time of design/construction but do not comply with current editions do not require upgrading.
As such anything that complied at the time of design/construction should only warrant a code C3.
As RCD protection for sockets which would reasonably be expected to supply portable equipment used outdoors was a requirement of both the 15th and 16th editions, it is unlikely that an external non RCD protected socket complied.

In such a situation I would use code C2 for all instances where RCD protection is now required.
 
What have people got against CU's with only 1 RCD... Some are making it sound like they trip every month....
How many people on here have a CU with just 1 RCD? How long has it been since it tripped? Mine has been quite a bit. A few years. When the daughter knocked her drink over which was above a socket..
 
What have people got against CU's with only 1 RCD... Some are making it sound like they trip every month....
How many people on here have a CU with just 1 RCD? How long has it been since it tripped? Mine has been quite a bit. A few years. When the daughter knocked her drink over which was above a socket..
It’s just that it’s poor design and doesn’t comply with BS7671.
 
It’s just that it’s poor design and doesn’t comply with BS7671.

I agree, it isn't the best design and it doesn't comply with the current regs, but it did when it went in.
 
My interpretation from what you have said is that not having an RCD in the fuse board is an advisory not a fail
Notwithstanding the fact that I haven't seen the installation in question I would almost certainly have issued an Unsatisfactory assessment in the absence of any 30mA RCD.
 
My understanding, is that installations which complied at the time of design/construction but do not comply with current editions do not require upgrading.
As such anything that complied at the time of design/construction should only warrant a code C3.
As RCD protection for sockets which would reasonably be expected to supply portable equipment used outdoors was a requirement of both the 15th and 16th editions, it is unlikely that an external non RCD protected socket complied.

In such a situation I would use code C2 for all instances where RCD protection is now required.
Rubbish. What about fused neutrals which complied when installed?
 
Rubbish. What about fused neutrals which complied when installed?
What about them?
What about the fact we are allowed to construct an installation designed to an earlier edition?
Don’t tell me that on the same day I complete an installation in accordance with BS7671, it doesn’t comply because a new edition was introduced last week.
 
You can’t be saying that you would only C3 an installation which employed a fused neutral as part of its fault protection?
However rare this might be.
 
You can’t be saying that you would only C3 an installation which employed a fused neutral as part of its fault protection?
However rare this might be.
As far as I am aware, BS7671 has only ever allowed single pole switches, circuit breakers and fuses to be installed in A.C. line conductors, and prohibits any such device (unless linked to all other live conductors) from being installed in earthed A.C. Neutral conductors.
I cannot imagine applying a code C3, it would either be a code C2 or no code at all.
 
Actually found this a couple of weeks ago and I thought it was dead until a time clock kicked in and livened it up. Does some external Christmas lighting supplies. 20180207_194305.jpg
 
Look it is like this - it probably did meet requirements at the time. Whether it does now or not maybe be the subject of debate, however, for your own and more importantly your tenant's safety fitting one would be a good idea, and not expensive, as you have seen. Do you know what one does? Like I said before the spark has probably been in this situation loads of times before and been completely ignored by penny pinching landlords. Or, there may also be a good reason, so if I were you I would just crack on. He has not taken the mick with his price, IMO. Who was it told you that it should not have failed anyway? Have they been to the installation and done another EICR??

It is this type of lazy approach to sparking that bothers me. Itnis not a given fact that just installing RCDs ‘make it safer’.

The ‘RCD everything’ approach without no design or thought behind it is not what we ahould be doing. We could just say ‘wire everything in SWA makes it safer’. Why do we not do this? Because we need to ise our skill and interpretation to determine if these extra precautions are actually needed.

In this instance a safe installation has been made less safe by installing an ‘up-front’ RCD which is not to Regs.
 
New posts

Reply to Test failed due to missing RCD in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
307
Hi all, Just done an EICR and all tested fine, until I got to the RCD's. It's a dual RCD board, not sure if it's TNCS or TNS as it's a top floor...
Replies
8
Views
1K
Hi all. I have a small question about inspection interval labels. We all know to fit one of these labels with the relevant date upon completion of...
Replies
10
Views
776
Doing a kitchen job for my daughter’s music teacher, who also happens to have been in my wife’s class at school. Nothing big… just a little...
Replies
2
Views
213
Hello. Non-electrician here. Failed an EICR yesterday as the electrician graded my consumer unit C2. Why C2 and not C3? He didn't say (and still...
Replies
22
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock