Discuss Test RCDs in the UK Electrical Forum area at ElectriciansForums.net

R

robertoj

Hi guys I have a question: how the tests carried out on the 500mA RCD would differ from those carried out on the 30mA for test sockets outlet protected by RCDs 30mA Any hints??

Im my opinion test instrument disply large value times???
 
No 5x tests for RCDs with an IΔn other than 30mA (the only exception being 10mA RCDs if used for additional prtoection).

Just as a matter of interest, do the majority of MFT's have the facility of testing 10mA RCD devices at 5X?? I don't generally use MFT's but i've come across dedicated RCD testers that only tests at 5X when set on the 30mA setting... Not sure if my CM500 has the facility or not, can't say i've ever used it on 10mA devices...

Thinking about it, that may of only been the case on the auto test position where the tester runs through the sequence from 1/2-1X -5X incorporating the 0 and 180 cycle positions....
 
Just as a matter of interest, do the majority of MFT's have the facility of testing 10mA RCD devices at 5X?? I don't generally use MFT's but i've come across dedicated RCD testers that only tests at 5X when set on the 30mA setting... Not sure if my CM500 has the facility or not, can't say i've ever used it on 10mA devices...

Thinking about it, that may of only been the case on the auto test position where the tester runs through the sequence from 1/2-1X -5X incorporating the 0 and 180 cycle positions....

My Metrel MI3000 seems to be able of individually testing 10, 30, 100, 300, and 500mA at half, x1, x2, and x5 rated current. I only generally use the 30mA auto test function on it though.
 
Just as a matter of interest, do the majority of MFT's have the facility of testing 10mA RCD devices at 5X?? I don't generally use MFT's but i've come across dedicated RCD testers that only tests at 5X when set on the 30mA setting... Not sure if my CM500 has the facility or not, can't say i've ever used it on 10mA devices...

Thinking about it, that may of only been the case on the auto test position where the tester runs through the sequence from 1/2-1X -5X incorporating the 0 and 180 cycle positions....

Yes mate, my Megger 1553 can test 5x on 10mA and 30mA. You can set it to test 5x on anything above but it will automatically prevent the test from taking place.

On the auto test function, it skips the 5x tests on 100mA and higher for both 0 and 180 cycles.
 
Of course if you wanted to test a 100mA RCD at x5 you could just do a 500mA test ;)

Speaking hypothetically of course, I'm not suggesting you should or would need to
 
Just as a matter of interest, do the majority of MFT's have the facility of testing 10mA RCD devices at 5X??

I think so. I have noticed when using others' Fluke MFTs on the auto range that it incorrectly does a 5 times test on the 100mA setting.
 

Reply to Test RCDs in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, There's 2 single fan ovens in the house my mother recently moved into. Posh elecronic AEG units. It's been sat empty for a year, so the...
Replies
19
Views
1K
I have got these questions on 2391-52 inspection and testing but can't remember option of 1st two questions. Please any suggestion will be...
Replies
2
Views
630
Hello! I've been racking my brain this evening about some RCD selections. I've been doing some work for a solar installer, and they've asked me...
Replies
5
Views
860
Hi all, Grateful for your expertise regarding my confusion on the below. Context: French rural domestic property Single phase supply, TT...
Replies
12
Views
2K
Hi all, New to the forum. I have been asked to look at this for one of our guys who's had an issue onsite after some electrical works had been...
Replies
4
Views
661

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock