Discuss Testing 110 Tx in the Electrical Forum area at ElectriciansForums.net
If it is SELV CT-E remember to test for continuity from centre-tap to earth, and ensure it is earthed when you IR test the primary to earth, in order to prove the insulation of the windings as well as the circuit.
As far as I know you test the primary side as submains and then has 2 circuits each at 55v to Earth . 16A fuse testing each line.
wheres the neutral Lol
Ps is there anyway of knowing what overloads are set at on a vsd
(RLV) isn't SELV
Reply to Testing 110 Tx in the Electrical Forum area at ElectriciansForums.net
We get it, advertisements are annoying!
Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.