Using a low ohm meter (or multimeter)Is it possible to place 1 probe on the incomming earth at the CU and the other probe on (disconnected) earth rod to get the resistance of the rod (minus the external earth path which forms part of the Ze, wander leads etc). I know its not the correct instrument to use however should this method not work?? After all, if we assume worst case the Ze is 0.35 including the line conductor. Has anyone tried this method? I dont have a ELZ instrument.:cool:
 
in a nutshell no!!!! you wont get a reliable reading if any If you can get an ELI tester you can use that (method 2 GN3)

Also i do dought if you will get a readng of 0.35 from an earth rod If there is a main earth rod is it a tt system? If so you are looking for a reading under 200ohms or lower as well as RCD protection on everything.
 
Last edited:

Reply to Testing Earth Electrode with low Ohm Meter in the Australia area at ElectriciansForums.net

Similar Threads

My brain has been exercised a bit by this. Am I on the right lines with this extremely simplified example: If we take: -TNCS installation with a...
Replies
11
Views
4K
Hopefully someone wiser than me can help explain some odd measurements I’ve taken at my own home. This is a long read, I’ve tried to give as much...
Replies
21
Views
4K
I need to clarify something that's rattling around in my head. I was taught when testing lightning protection systems that the maximum...
Replies
11
Views
3K
Hi all, 99.9% of my work is TNS or TNCS but I am currently working out of my normal area at a property that is presumed to be TT (I say presumed...
Replies
2
Views
2K
H
Earth Electrode Resistance Testing 2395 Hey guys, I'm up for my 2395 soon, although I understand how each of the three methods is carried out I...
Replies
4
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock