  1. DirtyDog368
    Offline

    DirtyDog368 Regular EF Member

    hello all,

    i just installed a new cu, which some of you may have read in another one fo my threads. everything was fine until i tried to connect one of the ligthing circuits to the board but it made the RCD trip every time.

    i did some reading and suspected the ole borrowed neutral dilema.

    Now i just want to run something by you so bare with me.

    Imagine the new cu is installed
    all circuits connected (except light circuit) and working fine
    connect earth to earth bar of light circuit and all ok
    connect nuetral to neutral bar and pop goes one of the RCDs
    connect nuetral to the other neuitral bar and pop goes the other RCD
    connect L1 to mcb and pop goes RCD
    connect L1 to another mcb on other RCD and that pops too.

    does this sound like borrowed neutral.

    I tried to connect linked circuits into one mcb and but its RCD still tripped.

    So i am thinking perhaps this is not a borrowed earth but perhpas insulation reistance problem. However the mcb never trips so if there is leakage of current it is too small to trip mcb but big enough to trip rcd.

    can any one suggest a test method to either prove or dicprove this.

    thanks very much


    DD368
     
  2. Knobhead
    Offline

    Knobhead Guest

    Standard IR tests, have you done them?
     
  3. DirtyDog368
    Offline

    DirtyDog368 Regular EF Member

    yes but how would the readings differentiate between IR problem or borrowed neutral scenario?
     
  4. telectrix
    Offline

    telectrix Scouser and Proud of It Trusted Advisor

    Top Poster Of Month

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    IR test each lighting circuit L/N, L/E, N/E, with all loads removed. bet you've got either a N/E reversal or a N/E short.
     
  5. andyb
    Offline

    andyb Electrician's Arms

    Location:
    West Sussex
    Think about what you are asking.
    The mcb is rated 6 amps & the rcd is rated 30ma

    An IR test will not highlight a borrowed neutral.
    If the rcd is tripping because of earth leakage due to low IR, that would of shown up with your testing before energizing the circuit.
     
  6. Rockingit
    Offline

    Rockingit Trusted Advisor

    Location:
    Somerset
    From experience, the first place I'd go looking is on the landing. 2way switch downstairs, probably a 2G along with another light thats on the downstairs ring, and the light on the landing is 2way switched but wired from the upstairs (or vice-versa). Easy way to test is to put both circuits on the same RCD and then go around the place a switch at a time.
     
  7. Jimmyb
    Offline

    Jimmyb Electrician's Arms

    Location:
    East Yorkshire
    turn all lights on then IR test between the live for one light circuit and the neutral from the other, if poor IR result go turn the lights off and IR test again if the results are now good then it a borrowed neutral, switch each light on one by one and test inbetween untill the problem one is found. it will prob be the landing light having the live fed from downstairs switch
     
  8. wirepuller
    Offline

    wirepuller Trusted Advisor

    Location:
    south uk
    Borrowed neutrals (or lives) can be identified by IR testing between circuits..(disconnected).....standard test proceedures ( continuity-polarity-IR) will identify any other problems before energising circuits.....swapping around energised circuits in the hope that trips wont trip is not the way to do it.
     
    • Like Like x 1
  9. ackbarthestar
    Offline

    ackbarthestar Trusted Advisor

    Location:
    A Zoo near YOU
    I can remember being shown that IR testing should be for both individual circuit and for separation of circuits, not only be between the P/N, PE/P and PE/N of each circuit but a basic IR/cont test between the neutrals of each lighting circuit and between the lives and the neutrals of each socket circuits. If there is a crossed neutral then that should pick up the problem.
     
    • Like Like x 1
    Last edited: Oct 15, 2011
  10. andyb
    Offline

    andyb Electrician's Arms

    Location:
    West Sussex
    No it doesn't (assuming you moved the neutrals over also)

    This proves it.

    Have you carried out an insulation test on these circuits? and if so what was the result?

    It seems that you are using trial & error to find the problem,
     
  11. GLENNSPARK
    Offline

    GLENNSPARK Electrician's Arms

    Location:
    west yorks.
    Rubbish.....you can IR between the neutral bars at 250V with lamps in and switches on.....if it comes back flat then you have a borrowed neutral ...thats assuming all other IR tests are good of course.....
     
    • Like Like x 4
  12. Big n Daft
    Offline

    Big n Daft Guest

    Is it me or is this all simle stuff that can be found using a test meter? The guy who started this thread needs to think if he's in the right game, trial and error is not good for fault finding.
    Stop think and do it to a logical system.
     
    • Like Like x 1
  13. andyb
    Offline

    andyb Electrician's Arms

    Location:
    West Sussex
    It's not rubbish Glenn
    When would you ever do what you say in a normal days work?

    The test you are talking about would show the same result in a continuity test between neutrals as well. Which is my rubbish point. A borrowed neutral would not show up during normal insulation resistance tests.
     
  14. ezzzekiel
    Offline

    ezzzekiel Guest

    to be honest apart from looking for link at downstairs switch dont usually bother checking for them, if it turns out to be there then a new cable is ran regardless so cant see the point.
     
  15. Inteificio
    Offline

    Inteificio Guest

    Am I missing something or is testing for a shared neutral simple?

    take a resistance reading from the relevant live and work your way down the neutrals and see which ones are connected. If there is more than one connection you have a shared neutral.
     
Loading...
Similar Threads - testing borrow neutral Forum Date
Lighting strike on property. high ZE and arking when testing. New Member Introductions Aug 10, 2018
Testing question EIC/minir works Electrical Course Trainees Only Aug 5, 2018
Thread Status:
Not open for further replies.

Share This Page

Users found this page by searching for:

  1. finding a crossed neutral

Electricians Directory Post a Domestic Job Post a Commercial Job