hello all, im a jib graded electrician just finished my 2392 course and have my 2391 course booked for the end of september. im pretty as green as grass as testing goes as i have not a great deal of experence. ive be asked to test a number of circuits and the sockets all have metal back boxes and are all earthed, making my r1 and r2 tests a nightmare because it is not practible to disconnect all fly leads conneting the earth to the backboxes to the steel and so on. i have got ok reading on the zs tests at each socket and measured the live to live neutral to neutal and earth to earth values on the dead tests. also ok readings on rcd tripping, and insulation resistance. so to sum it all up i havent got a correct value fo the r1 and r2 figure of eight loop on the dead tests. is this a problem? do i have to dissconnet ALL flyleads and possible parrell paths?


ps sorry im not that great at explaning things
 
you do not need to dis the flyleads. just cross connect the L and E 's at the CU and get your R1+R2 readings from each point. ( notice the use of caps. R1 and r1 are completely different values)
 
If this is not an initial certification, R1+R2 is not required, just Zs.
If it is an initial certification, the fly leads will be required to be dsconnected, and R1+R2 will have to be measured and recorded.
 
ok thanks for the reply, by cross connect do you mean the figure of 8 loop method? ive tried that method by cross connecting the opposite legs, then i try on the same legs and still seem to get the same reading at each socket, is this due to parallel paths?
 
you should get tha same readings at each socket. it's because it's cross connected ( figure8 ). only time your readings will be higher is if you've got a spur or a poor connection.
 
If you are a bit green with testing and you are doing the 2391 this month then getting GN3 now and getting stuck in is a must. The more of GN3 you can digest the easier it will be. As for the practical don't dwell too much you will be walked through it during the course, but a good read and study of the test procedures will stand you in good stead.

Cheers...........Howard
 

Reply to testing issues in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
783
Hello all, I hope you're all keeping well. I have a question regarding insulation resistance testing. Whether doing a single circuit IR test or...
Replies
9
Views
565
Hi all, We have a limited in house PAT testing requirement and were advised that the TIS700 fitted our needs. The unit works fine for 110V and...
Replies
0
Views
646
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
Good day. First time poster. We recently had an electrician perform the EICR, as this is a newly purchased property I thought'd I would have the...
Replies
7
Views
692

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock