eagleeye

I have just finished a rewire in wales. All the circuits tested out ok. but as i have never done a test on a tt system i was a bit confused on the reading for the earth loop impedance tests. The test on all circuits were coming in around the 15 ohm mark as did the Ze. is this correct or have i made a mistake. All main bonding conductors were disconnected with only the earth rod connected
 
You are correct
A reading of 15 ohms for a TT system is an excellent result,considering up to 1667 ohms (30 m/amp)is ok
The wiring regs recomend a reading of under 200 ohms.so you are way within whats required

Remember the Zs figures in the big red book refer to TN systems
 
As said that is a very good result. Round my way most of the results I get on TT systems are 150-175 Ohm range.

You have carried out the test correctly as well from what you have written, the only other way of testing a TT system is with an Earth Electrode Resistance Tester and that will take you a while because of having to install another 2 temp rods to test.

I always carry out the test the same way you have listed above ;)
 

Reply to testing on TT system in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Carrying out a EICR in a commercial setting. In the main intake room the DNO supply comes in and it states clearly this is a PME system. 5 years...
Replies
5
Views
1K
Hi, I did my first EICR on a TT system today and the Zs was a lot higher than Ze+R1+R2 on everything. Zs was around 3.5 ohms on all of the ring...
Replies
10
Views
971
OLDBOY
O
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
Hope this all makes as much sense as i can make of it and my "problem" can get sorted via some guru on here... Just a quick background on myself...
Replies
4
Views
916
Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
Replies
20
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock