Discuss Testing query???? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

C

Canttouchthis

Whilst carrying out a periodic inspection today I stumbled across something I've not seen before a 2 gang metal back box fixed to a finished wall with a plastic socket on it? Strange I thought hears were I'm unsure! I checked the socket over all was well and the back box was earthed as expected so is this something I could note down using the 1-4 coding system or is it fine but just a little bizzar. What do you guys think?
 
do you mean a surfasce mounted metal box? if it's safe, it's unusual but compliant so no code.
 
Hi,
is this a metal clad back box, or a back box that would normally be chased into a brick wall ?

If its the later, I would put it as a code 2, due to the fact the knock outs on the tops and the sides can be easily removed and hence expose the wiring to touch.

If its just a metal clad back box, then code 4
Hope this helps,
Sav
 
yep, if it's a knockout box,surface mounted , a code 2 IMO.
 
Well all reg 530.4.2 tells us that a socket outlet must be fitted to an appropriate mounting box and a flush back box does fit the requirements as a BS 4662, though agreed a BS 5733 is more the norm.

So our task should be , where does it contravene the regs?
 
IP rating if a knockout is dislodged. just plain unsafe. IMO. apart from looking like a pig's breakfast
 
could always wrap a bit of tape over the holes.!
 

Reply to Testing query???? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hello everyone, Following on from my previous post where I received advice on taking a spur off a 40a feed (thank you). I performed the work...
Replies
4
Views
843
Hi, I swapped a 2 gang switched socket for a 2 gang switchless socket with usb ports downstairs. I switched off all the power to the house by...
Replies
8
Views
764
I am wiring up a new kitchen and conservatory. I'm not sure why I checked continuity between line and the metal back box of the light switch, but...
Replies
3
Views
715
Hi, This post is about my concerns with medical IT socket outlets and want to alert you all if you are fitting them in a hospital. The current...
Replies
20
Views
2K
An odd question granted but bear with me. I've got to extend a radial circuit in a community centre to fit a new hand dryer in the toilets, but I...
Replies
15
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock