0
Hi,
An old customer has asked me to run a health check on their Solar PV system which we installed some 5 years ago. Not something I've done before, beyond the standard installation testing, so I was going to:
  • Test each panel for Vout against irradiance
  • Check all electrical connections
  • Test the inverter.. somehow!
They want to move to micro inverters but I'm saying that if the existing string inverter is still working they should run with that until it pops. Any thoughts on how I can test their inverter, show its still being efficient etc? I was hoping to maybe test DC in v's AC out and run a quick % calc. What do you think?

Thanks in advance for any advice!
 
I used to do a bit of maintenance/service calls on solar systems and all we did, was same tests as when you install it. Waste of time testing individualy imho. Have a quick look through the history on the inverter to check it hasn’t been dropping out. Sounds like these people have money to burn if they want to start changing things after 5years?!
 
I'll see if i can get any logs off the inverter but was looking to test efficiency, if I can.

Any thoughts on testing efficiency? If I get DC total in and AC out what could I derive from those numbers?
 
When we do 'health checks' for people buying a house with PV, we do a full standard installation commissioning check, Voc, Isc, Irradiance, Resistance to earth, cable routing, condition, component rating, labelling etc.
And have come a cross a few nightmares, like 6mm AC T&E used for the DC from inverter to loft, AC isolators instead of DC etc, inverters mounted on non fire resistant boards etc.
Then look at their generation meter returns to their FiT supplier - they'll have quarterly logs, (and what the inverter logs say) then knowing the installation postcode, elevation, orientation, and a shading analysis, compare that to the MCS predictions (they should over time be within 10%) compare that to the original predictions given to the client at quotation stage and in the handover pack.
Also go to PVoutput.org and see if anyone locally is logging daily outputs and compare those to the installation.
 

Reply to Testing the Inverter in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

Hello All and happy new year. Over the holiay I have changed all of my old sockets to some nice new ones and added a couple with usb sockets for...
Replies
4
Views
737
Hello there I have just installed a new Solis S6-GR1P3.6K-M-DC Inverter - this replaced a 10 year old+ Sungrow inverter that failed/out of...
Replies
5
Views
2K
Hello everyone, I'm currently working on a project to upgrade an existing renewable energy system and could really use some expert advice. The...
Replies
0
Views
641
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
405
Hi everyone, this is my first time using a forum so please don’t criticise to much. I recently done by EESS course but I didn’t actually find it...
Replies
4
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock