No mate, it is because PEFC is taken with all bonding conductors and CPCs connected, Ze is taken with the Earthing conductor disconnected from the rest and measured on it's own.

PSSC is a different measurement. ;)

In principle then, the earth loop resistance with the earthing conductor connected may be lower due to parallel paths; therefore, the PEFC may be higher. The same measurement configuration for the meter, but 2 different configurations for the electrical installation. Ze without earthing conductor connected, and PEFC with the earthing conductor connected!

Hope that is correct, thank you for refreshing my memory or correcting my understanding!
 
No mate, it is because PEFC is taken with all bonding conductors and CPCs connected, Ze is taken with the Earthing conductor disconnected from the rest and measured on it's own.

PSSC is a different measurement. ;)

Indeed, and the Prospective Fault Current (PFC) is the greater of the PEFC and the PSSC. It's amazing that people think that PFC is synonymous with PEFC or PSSC. (Not directed at you as you clearly understand the difference!)
 

Reply to Testing ze at the origin in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Fluke MultiFunction Tester 1662 TNS Earthing system. Switchboard - 415v - 3 Phase + Neutral + Earth. MCB 1000A 3 individual Earths (185mm)...
Replies
22
Views
3K
Hi all, We have a limited in house PAT testing requirement and were advised that the TIS700 fitted our needs. The unit works fine for 110V and...
Replies
0
Views
656
Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
535
When I joined this forum a decade or so back, there was a discussion going on about a welder that was connected with a 3-core cable to L1, L2 and...
Replies
3
Views
2K
In my line of work it's very rare that I ever have to change a DB. I'm largely in maintenance; occasionally have to add new circuits etc. so in...
Replies
3
Views
621

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock