Discuss testing Zs and Ze in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

zone77

-
Reaction score
0
when i measure Ze from a DB ( disconnecting main bonding) am i suppose to reconnect bonding b4 testing Zs on final circuits. on job 2day some Zs from sockets was lower than Ze:confused:. i put this down to parralell paths but am i doing it correctly??
 
when i measure Ze from a DB ( disconnecting main bonding) am i suppose to reconnect bonding b4 testing Zs on final circuits. on job 2day some Zs from sockets was lower than Ze:confused:. i put this down to parralell paths but am i doing it correctly??

As soon as you have done Ze reconect main earth before doing any Zs tests ( paralell paths will influence Zs)
Paul
 

Reply to testing Zs and Ze in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
772
Evening everyone, I was taught when carrying out Zs testing to test both L-PE and L-N and record the highest result of the two tests for my Zs...
Replies
11
Views
2K
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K
I just finished a garden room supply. The customer already had a CPN garage consumer unit that the last sparks left there, brand new in box, and...
Replies
2
Views
844
Got my am2 coming up on Tuesday and I know I have to calculate my Zs readings Maybe I’m overthinking this but am not sure if I need to use the Ze...
Replies
17
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock