Discuss the importance of zones in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
92
Hello guys

something quite odd occurred , the job at hand had been to install a main bond to the gas pipe however on this occasion after checking the zones i saw no plausible reason for a cable to be in the location i had been about to drill.
i drilled a small pilot and during this i smelt carbon which immediately rang an alarm bell.
I check all sockets and the power was fine and no BS 3036 fuses has blown.
long story short i just about nicked a T&E cable which ran diagonal across the room, not an issue as i repaired the cable.
i checked the 3036 fuse and nothing had blown however quite a bit a black carbon i found whilst repairing the cable.
carried out all the tests and replaced fuse wire just in case, has anyone grazed a cable before and not blown the fuse? very strange as i ran a Zs off the circuit once repaired and all was fine on the earth fault loop.
The short had been between the line and earth
 
Last edited:
Has anyone used cable tracers for walls, first time in 10 years catching a cable... are they any good?

I've got a Bosch blue one, which is pretty good and seems to have a good depth of pickup. Results I would say are mixed in that it can, by virtue of being sensitive, lead you to being very cautious.

As an example, I used it when fitting some exterior lights. The house had recently been rendered, the cables for the lights had been fitted by another spark prior to rendering and my client didn't know where they ran so I had to be very careful fitting the lights. I spent an age trying to locate them because in some places it seemed to be picking up all sorts of metalwork making it very difficult. In the end I located the places with the weakest signal and took a punt.

Edit:- I should add, I didn't hit anything :)
 
I have one, and unfortunately it's next to useless ... It will reliably find metal capping. But if Last Electrician has used metal capping, then it's probably in the right place so I don't need help to find it. Maybe expensive ones work better?
 
I have a Bosch green one (diy version), and dependant on what day of the week it is and if there's an 'r' in the month, it will pick up the presence of metal or electrikery. The rest of the time it goes off at the merest hint of a piece of a wet lettuce.

The only remotest use for it I've found, is trying to trace the route of a cable. I'm led to believe if you pay for one of the very expensive professional versions (blue) they are more accurate (but not according to SC experience).
 
The only remotest use for it I've found, is trying to trace the route of a cable. I'm led to believe if you pay for one of the very expensive professional versions (blue) they are more accurate (but not according to SC experience).

In terms of finding stuff, it's fantastic, but I reckon it's probably capable of finding capping on the other side of the wall, so in that respect it's a little too sensitive. However, it does provide quite a bit of visual feedback which can be used to give you a hint. It has a couple of bar type items on the display IIRC that vary in size based on proximity. Sometimes it's a matter of getting them as small as possible rather than a green light.
 
My 3 top tips:

1. safe "zones" are a relatively new invention

2. Only sparks really understand them

3. Never assume cables run in zones, especially in older properties
I used to give customers a printed diagram after larger jobs so they knew where the zones were, I thought it a good idea at the time. Then one bloke rang up saying he had put a nail through a cable in the other part of his house, and it was not in one of "my" zones, and it's all my fault so can I come and fix it FOC. I don't do it now.
 

Reply to the importance of zones in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I had an interesting little job this morning. Three sockets in an extension were not working and haven't worked for quite some time (years). It...
Replies
0
Views
228
Hi, Just been scratching my head about this one and wonder if I've missed anything. A few weeks ago I installed a new circuit for a 3kw oven and...
Replies
6
Views
738
I'll start by saying - I have absolutely no intention of doing any wiring or anything electrical myself. You get someone professional to do a...
Replies
8
Views
779
Bit of a long shot on here but does anyone have a circuit diagram for a Chavin Arnoux CA 6545 5kV tester? I've copied my post on EEVBLOG forum...
Replies
0
Views
370
A BG fused connection unit, with neon. A boiler. Fuse out. Spur switched off. I was checking polarity after a colleague had 2nd fixed it and...
Replies
7
Views
709

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock