Posting a message to the forum will remove the above advertisement
  1. This site uses cookies. By continuing to use this site, you are agreeing to our use of cookies. Learn More.
  2. angel While you're here, would you mind checking out our Electrician's Insurance section to see if we could save you a few quid? - Specifically our Van Insurance Deals and Public Liability Insurance Deals. Thanks for supporting the forum! angel

    5% Discount from Electrical2Go.co.uk for ALL members! - Click Here

  3. Forum for Trainees.

    If you are a trainee and haven’t already applied to join our trainee forum then click HERE The trainee forum is a closed area of the forum where the Forum Mentors will freely share their vast experience within the industry. 

    Dismiss Notice

Discuss The never ending Assessment Installation. in the Electrical Forum area at ElectrciansForums.co.uk.

Thread Status:
Not open for further replies.
Please make sure you checkout our forum sponsors, many do discounts for members and, they keep the forum free to use.
  1. wcampbell
    Offline

    wcampbell Guest

    Hi all.

    I'm working on my second of two assessments ( I'm a novice ).
    So far I've sorted new E Tails to metal socket plates, sorted reverse polarity at cooker isolation / socket switch ( still don't understand why fridge has n't got a problem with phase in neutrals at switch! ), got all the results for the EIRC, and fitted a new CU.

    My ( hopefully ) last problem concerns main bonding as follows:

    Cut 30' ish of 10mm E. Tested ends and got a continuity reading of 0.02ohms.
    Fitted cable in situ ( clamp at water stop, then through wall to clamp at gas mains ( cable not cut ), then back into house to CU.

    About five feet of this run sees cable running parallel in conduit and wall.

    Now when I carry out continuity of main bond I get -00 ohms.

    I have tested with leads not nulled and get a reading 0.02 ohms lower.

    Is the parallel section causing this?

    I know the reading must be below 0.05ohms but surely there must be some resistance.

    How will this look to the assessor?

    Thanks. :nonod:
     
  2. jimmymac
    Offline

    jimmymac Electrician's Arms

    Location:
    Scotland
    0.02 ohms is probably as low as your tester will measure. If there is a parallel path you will get different readings
     
  3. rich.250
    Offline

    rich.250 Electrician's Arms

    Location:
    Cornwall
    Business Name:
    Rich Williams Electrical
    Have you disconnected the db end from the MET? If not there may be a parallel path??
    Myself I would be thinking that that is on the limit of 10mm to meet .05

    Are you testing this with a r2 lead or equivalent?
     
  4. wcampbell
    Offline

    wcampbell Guest

    Thanks for your reply. Testing with Kewtec Continuity Tester with the usual red / black crocs. Main Bond is not in MET yet. 10 mm Bond tests -00ohms when disconnected from clamps.
     
  5. rich.250
    Offline

    rich.250 Electrician's Arms

    Location:
    Cornwall
    Business Name:
    Rich Williams Electrical
    You want to test it when it is all inn-situ.
    Then disconnect from Met. One clip to 10mm other to r2 lead that is connected to clamp.
    Then remember to remove lead resistance. If your not sure, follow the GN3 is the Best advice I can give you.
     
Loading...
Similar Threads - never ending Assessment Forum Date
Help! Never seen this before! Electrical Forum Oct 11, 2018
Well I would have never thought it---- Politics & The Economy Sep 21, 2018
Thread Status:
Not open for further replies.

Share This Page

Electricians Directory Post a Domestic Job Post a Commercial Job