Hello guys

got a question relating to lighting dimmers
I have been asked to install a 24 way Stage lighting dimmer and each circuit is 10A running around 50m to each socket, the cables will be housed In 100 x 100 trunking, I am just little confused at the groping factors as not every circuit will be used at the same time and what is used will be on at say 60% per circuit.

do I apply the 0.38 grouping factor as there is over 20 circuits or can It be less as only 50% to 60% of he 24 circuits will be used at any one time??

there is also probably 6 other power circuits in the trunking

Let me know what you think
 
I am just little confused at the groping factors

I've never been able to get a firm grasp of them either!

The supply capacity to the dimmers might limit the total possible number of fully loaded circuits. This is always the worst case - a larger number of circuits with less load per circuit, totalling the same load, will cause less heating per unit length of trunking. Depending on venue application you may be able to apply diversity based on bar loadings and/or on specified fixture types, but for some systems that is not permissible because of the expectation that a whole block of circuits will be fully loaded. At 50m voltage drop might just start to play a part in your cable choice. Each situation is different and it requires some specialist knowledge.
 

Reply to Theatre Lighting Dimmers in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I am looking at installation of an architectural dimmer, that is will supply 6 channels, with 20A circuits each (2400W ea). Our hall has can light...
Replies
2
Views
670
Hi all, Just to be clear, I'm not looking for advice on upgrading but rather just clarification of our existing setup. We need to upgrade the...
Replies
12
Views
1K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
Hi guys I have been tasked with upgrading some old rewireable fuseboards for a food warehouse that runs continually 24/7. I was asked to do an...
Replies
10
Views
2K
Hi all, Grateful for your expertise regarding my confusion on the below. Context: French rural domestic property Single phase supply, TT...
Replies
12
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock