Discuss This could be tricky to upgrade... in the UK Electrical Forum area at ElectriciansForums.net

O

Octopus

Been doing a partial EICR today due to a muppet changing a fuseboard, no certs, no invoice, very shoddy installation flagged by a visiting air conditioning engineer!

This is a picture of the service head ............. the main earth needs upgrading to 10 or preferably 16mm - but is it possible?

Kay 1.jpg

This is the CU end of the gas bonding!


Kay 2.jpg

Thoughts?
 
You could if you can get one of those round solid copper bars some CUs use to link the neutral bar to the rcd. Form it nicely, sleeve it and fit another terminal. Alternatively get the DNO to fit another terminal.
 
Maybe remove one or two of the existing screws, drill one of the existing holes out to a 5mm hole all the way through the block and tap a 6mm thread. Crimp a 16x6 lug onto a piece of 16mm earth wire and bolt it into the newly made hole. Then just mount a new earth bar in a more accessible place.
 
If you're hesitant to get involved with dentistry type work of drilling and tapping holes I guess you could also remove the earth wires that are in the termination block, fit 3x new 6mm wires into it and use them in parallel to supply a new, more accessible termination block into which you connect the two wires you removed.
 
Maybe remove one or two of the existing screws, drill one of the existing holes out to a 5mm hole all the way through the block and tap a 6mm thread. Crimp a 16x6 lug onto a piece of 16mm earth wire and bolt it into the newly made hole. Then just mount a new earth bar in a more accessible place.

Sounds like a pretty good plan!
 
In a similar vein to Marvo, it looks like you have a 10mm² and a 6mm² in the block at the moment so if you were to use those two and cut them and reterminate into a new earth block you would have a 16mm² from earth block to head and could then terminate your new conductors earthing and bonding into the new earth block.

Then again someone managed to get that later cable in place, but possibly at change of service head.
 
And in another similar vein you could also connect a lugged 16mm to an existing terminal screw on the block, with a washer if necessary.
 
In a similar vein to Marvo, it looks like you have a 10mm² and a 6mm² in the block at the moment so if you were to use those two and cut them and reterminate into a new earth block you would have a 16mm² from earth block to head and could then terminate your new conductors earthing and bonding into the new earth block.

Then again someone managed to get that later cable in place, but possibly at change of service head.

Sadly they are 6 & 2.5mm
 
I very much doubt you could lug a conductor onto the block even if you drill and retap it and hope it remains secure without movement unless the lug has two termination holes. It is also ad hoc and not the recommended means for terminating a conductor at that style of block.
 
Last edited:
I like the idea of the three 6mm in parallel , but im not sure how you work out that it would be the equivalent to a 16mm , i don't think you can just say 3 x 6 =18mm
 
If the wooden panel, on which the service head is mounted, could be released, and without, of course, putting any strain on the incoming service cable could the panel be lifted enough to winkle a conductor into the terminal?
 
If the wooden panel, on which the service head is mounted, could be released, and without, of course, putting any strain on the incoming service cable could the panel be lifted enough to winkle a conductor into the terminal?

Quite possible - not been asked to quote for remedials as yet .... so not really thinking about it..
 
You can just times it by three, the calculation for csa only changes by adding n which is number of conductors.
 

Reply to This could be tricky to upgrade... in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Can someone sanity check my thinking please.... An 80 amp PME service head, tails to meter, 25 sq mm tails into an enclosed fused isolator with...
Replies
4
Views
1K
Hi all, I am looking for some advice regarding old rewireable (3036) fuse boards in regards to additions and alterations. I am an electrician and...
Replies
28
Views
4K
Hi folks, first time poster and soon-to-be landlord's assistant (letting my partner's property out now that she's moved in). We've just had a new...
Replies
70
Views
8K
Hi I don't know if I should ask it here or the main electricians forum. It's about CU change and the work around it and the CU change will be done...
Replies
78
Views
11K
One of the oddest jobs I've ever had today. Called by a plumber I know who had attended after a leak through the kitchen ceiling from bathroom...
Replies
24
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock