I'm going out later today to quote for installing a kiln in a customers garage.
He has sent me the specs for the kiln and photos of his consumer unit. He tells me that the only other heavy load item is a 10.8kW shower.
The run from the CU to the garage is approximately 25 metres
The kiln is rated at 50 amp / 11.5kW
The CU is split load RCD with 2x 32 amp ring finals, 2x 6 amp lighting and 1x 40 amp shower circuit.

I think the fuse fairy will need to check the DNO fuse size to see if it will cope with the load

I am thinking 10mm2 T&E or SWA depending on routing of the cable
Not sure whether to install separate CU for the kiln (splitting the incomers with Henley block), need to calculate the loads but think this may be better than potentially overloading the current CU.
What would you recommend for connecting the kiln, I initially thought of a commando socket but have only seen them to up to 32 amp.

Any thoughts would be appreciated.
 
No mention of electric cooker in the house, so loadwise it’ll be ok.
Just don’t have a shower on at the same time.

Install a heat exchanger and heat the rest of the house from the garage.
 
Been out to quote. The fuse fairy tells me there is a 100 amp cut out fuse. The hob is gas and the oven is 3.5kw on a 13 amp plug so load wise I think they will be fine (need to do all the calcs yet)

The only potential issue is the property is a semi on a looped service, theirs being the first. Is it worth discussing with the DNO as I do not know what sort of load the other property will be pulling..

upload_2019-1-18_14-27-29.png
 
do the job first. then let DNO worry if there's a problem. if you contact them first, your client might face a huge bill for modifying the service.
 

Reply to Thoughts on kiln installation in customers garage in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello All, new to the forum. Would be grateful for advice on whether the following proposal is an acceptable solution or open to any suggestions...
Replies
9
Views
5K
Hi all, My question relates to the omission of overcurrent protection (specifically overload and fault protection) at the origin of an...
Replies
6
Views
2K
I'm planning a replacement for my existing domestic CU and would like to have it sanity checked before I get an electrician involved. The main...
Replies
33
Views
4K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
So a customer had a nuisance trip and I spent 4 hours trying to find the fault (first hour identifying circuits as none labelled at board). There...
Replies
18
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock