Posting a message to the forum will remove the above advertisement
  1. This site uses cookies. By continuing to use this site, you are agreeing to our use of cookies. Learn More.

Discuss Three Phase overhead supply is it TN C in the Periodic Inspection Reporting & Certification area at ElectrciansForums.co.uk.

Please make sure you checkout our forum sponsors, many do discounts for members and, they keep the forum free to use.
  1. Michael J
    Online

    Michael J Michael J

    Location:
    Swansea
    While carrying out a EICR I found on first inspection that there were no RCDs installed . When I checked at the Pole Mounted Transformer the Earth & Neutral were connected at the Neutral point. So am I right in concluding it's a TN-C System? The 17th Edition states that RCDs should not be installed where a TN C System is used (411.4.4)
     
  2. buzzlightyear
    Online

    buzzlightyear please let me back in to the prison cell.

    Location:
    star command
    Are you sure it is tncs on the pole or TT.what is in the property?.
    got any pic of the board .
     
  3. Michael J
    Online

    Michael J Michael J

    Location:
    Swansea
    I will take a pic tomorrow,but it looks like the Earth and Neutral are connected at the transfer. The reason I am suspecting is a TN-C is the lack of RCD protection on the Ring main final circuits. If it was a TT it would be protected with RCD at the mains
     
  4. buzzlightyear
    Online

    buzzlightyear please let me back in to the prison cell.

    Location:
    star command
    you mean up front RcD Before the main switch .
     
  5. Michael J
    Online

    Michael J Michael J

    Location:
    Swansea
    Yes, or any final circuit in the building, by the way it feeds a hotel. The overhead feed is by way of bundle conductors (4) sorry that's a South African term. I don't know what you call them here?
     
  6. buzzlightyear
    Online

    buzzlightyear please let me back in to the prison cell.

    Location:
    star command
    is it three phase to the buiding.
     
  7. Archy Styrigg
    Offline

    Archy Styrigg Forum Mentor

    Location:
    Manchester
    Eh?
    The 17th Edition states that RCDs should not be installed where a TN C System is used 411.4.4

    The following types of protective device may be used for fault protection:
    (i) An overcurrent protective device
    (ii) An RCD.

    It'll be a PME supply. Concentric cable split at the installation intake, to N & E.
     
  8. Michael J
    Online

    Michael J Michael J

    Location:
    Swansea
    Read on a couple of lines after Note 1
    "An RCD Shat be used in a TN-C system"
     
    • Funny Funny x 1
  9. Michael J
    Online

    Michael J Michael J

    Location:
    Swansea
    Sorry guys it's late it should read " An RCD Shall not be used in a TN_C system":oops:
     
    • Funny Funny x 1
  10. Michael J
    Online

    Michael J Michael J

    Location:
    Swansea
    Yes it is
     
  11. Archy Styrigg
    Offline

    Archy Styrigg Forum Mentor

    Location:
    Manchester
    I think you might be getting confused here chief, TNC is NOT allowed within an installation. TNC/PME supply, then the Earth is split off at the intake.
     
  12. Strima
    Offline

    Strima Electrician's Arms

    Location:
    St Neots
    That'll be 414.4.5 for no RCD on TN-C?
     
    • Agree Agree x 1
  13. buzzlightyear
    Online

    buzzlightyear please let me back in to the prison cell.

    Location:
    star command
    take pic for us in the main intake at the hotel.
     
  14. buzzlightyear
    Online

    buzzlightyear please let me back in to the prison cell.

    Location:
    star command
    Strima are you not counting sheep in your bed .LoL .because im in night garden with iggle piggle.;)
     
    • Informative Informative x 1
  15. Michael J
    Online

    Michael J Michael J

    Location:
    Swansea
    Thanks, I will take a closer look at the intake, I just don't understand why there are no RCDs on the final ring circuits this hotel has 6 DBs
     
Loading...
Similar Threads - Three Phase overhead Forum Date
For Sale [North]: Single Phase & (some) Three Phase Boards & Devices For Sale and Wanted Forum Jan 4, 2019
Connections of a Three phase Motor STAR and DELTA. Electrical Wiring, Theories and Regulations Dec 31, 2018

Share This Page

Electricians Directory Post a Domestic Job Post a Commercial Job