Discuss Three phase solar in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

L

Lcfcbunny10

Starting a solar three phase project, how do you connect the generation meter from 8 three phase inverters, or will each inverter have it's own g meter? Appreciate a response
 
Possibly as above , but this does depend on many factors .
For a start what size of system is it , what type of install / environment is it , and what size and type of inverter are you using ?
 
As above, AC DB with suitable OCPDs, CT-set, kWh meter suitably scaled. Watch out for any required RCD protection and Section705 requirements, particularly when using TL inverters. Carefully consider surge/lightning protection requirements and any subsequent impact on aforementioned RCD selection, if applicable.

Also consider whether the possible requirement (dictated by the DNO) of an external G52/2 relay might open up options for integration of AC DB/protection into the G59 enclosure.

HTH
 
Starting a solar three phase project, how do you connect the generation meter from 8 three phase inverters, or will each inverter have it's own g meter? Appreciate a response
step 1 - talk to andy at sibert.

step 2 - buy the kit recommended from him

step 3 install it.

andy's got a good range of the kit for this sort of situation and knows his stuff.
 

Reply to Three phase solar in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

Hi I have three phase installed recently to increase generation. DNO approved the extra 2 solar arrays so we have 3.68KW FIT on one phase and 8KW...
Replies
1
Views
685
I currently have solar array and was going to purchase Shelly EM to monitor Grid in/out and solar production. So far so good. But I also plan in...
Replies
0
Views
1K
I don't "do" solar, but I've been asked to comment on an aspect of a new domestic solar installation by others. There is no overload or fault...
Replies
7
Views
1K
I have a scenario where there is a three phase DB in a commercial property where there are mixture of three phase and single phase washing...
Replies
2
Views
828
Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock