    Your carrying out an eicr on a domestic property with a time delay 100mA RCD protecting lighting cables within 50 mm of the surface.
    What code would you give it c3 or c2?
     
  2. Pete999
    Offline

    Pete999 Trusted Advisor

    Top Poster Of Month

    Location:
    Northampton
    What do you think and why
     
    • Like Like x 5
  3. spinlondon
    Offline

    spinlondon Trusted Advisor

    Location:
    Harlow Essex
    If the cables do not have another acceptable method of protection, and they are run in prescribed routes, code C3.
     
  4. Vortigern
    Offline

    Vortigern Electrician's Arms

    Location:
    England
    Business Name:
    F.H. Electrical
    What system? Anyway C1
     
  5. Ian1981
    Offline

    Ian1981 Electrician's Arms

    Location:
    North east
    Cables buried less than 50mm from surface require protection by mechanical protection such as earthed metallic conduit ,swa etc or be installed with additional protection by an rcd.
    Only a 30ma rcd offers additional protection in this manner.
    The OP needs to decide if indeed it's a C2 which is potentially dangerous or C3 requires improvement to make it safer.
     
  6. westward10
    Offline

    westward10 In echoed steps I walk across an empty dream. Electrician's Arms

    Location:
    Northamptonshire
    You been at the undiluted Ribena again.
     
    • Like Like x 2
  7. Vortigern
    Offline

    Vortigern Electrician's Arms

    Location:
    England
    Business Name:
    F.H. Electrical
    HEhe yeah, well he didn't say buried in walls so I imagine they are floating around in the air.
     
    • Like Like x 1
  8. EMMEC
    Offline

    EMMEC Regular EF Member

    Location:
    London
    Business Name:
    EMM Electrical Contractors LTD

    I like Your comments :))
     
    • Like Like x 2
  9. Wilko
    Offline

    Wilko Electrician's Arms

    Location:
    Berkshire
    Business Name:
    Wilko Electrics
    RCD protection for cables in walls came in with 17th IIRC (?) so if it was built prior and it's in good condition etc then isn't it a C3 at most?
     
    • Like Like x 1
  10. Rpa07
    Offline

    Rpa07 2000 posts - only 46379 behind Telectrix! Electrician's Arms

    Location:
    Bristol
    Business Name:
    Ebenezer electrical
    He's the only one!
     
    • Like Like x 1
Loading...
Similar Threads - delay RCDs cables Forum Date
New MK RCDs tripping too high The Electricians Arms Aug 26, 2017
Academic questions regarding rcds. Electrical Wiring, Theories and Regulations Aug 7, 2017

Share This Page

  • Electricians Directory Post a Domestic Job Post a Commercial Job