Posting a message to the forum will remove the above advertisement
  1. This site uses cookies. By continuing to use this site, you are agreeing to our use of cookies. Learn More.

Discuss Timeguard rcd socket won’t trip with tester. Help please in the Electrical Forum area at ElectrciansForums.co.uk.

Please make sure you checkout our forum sponsors, many do discounts for members and, they keep the forum free to use.
  1. dnjr
    Offline

    dnjr Electrician's Arms

    Location:
    South coast
    Dear All
    Installation tncs. Wyler re-wireable fuses
    I’ve fitted 2 x timeguard rcd sockets to provide protection for extension leads going outside but neither will trip with my tester. Trip fine on test button
    Also trip when I do earth loop test ( fluke tester)
    Socket tester says it’s all ok
    Zs before I changed to rcd socket was 0.45
    Doesn’t trip on ramp test
    Ze 0.21
    What the hell am I missing

    Advise appreciated
    Cheers
     
  2. Strima
    Offline

    Strima Electrician's Arms

    Location:
    St Neots
    Circuit IR results?

    Does your test meter trip other RCDs?
     
    • Agree Agree x 1
  3. dnjr
    Offline

    dnjr Electrician's Arms

    Location:
    South coast
    Hi strima
    Yep works fine elsewhere. Never used these red sockets before. Wondering if I’m missing something.
     
  4. Risteard
    Offline

    Risteard Respected Member

    Location:
    Derry, Ireland
    Business Name:
    Walsh Electrical Services
    I've come across faulty SRCDs out of the box before. Obviously without having seen the installation I can't say that this is the case here but certainly it is possible.
     
  5. Pete999
    Online

    Pete999 Forum Mentor

    Location:
    Northampton
    Business Name:
    None
    Do they trip on the test button?
     
  6. dnjr
    Offline

    dnjr Electrician's Arms

    Location:
    South coast
    Hi Risteard
    I thought of faulty rid but to have two , one single socket one double would be very odd. I rang timeguard and they said it was possible so am getting two more from wholesaler but don’t expect it to cure it
    To be honest I was expecting someone to rip me a new one and say I’d missed something obvious
     
  7. dnjr
    Offline

    dnjr Electrician's Arms

    Location:
    South coast
    Hi Pete

    Yep work on test button

    Also forgot to say. IR tested before I changed them and all good
     
  8. Pete999
    Online

    Pete999 Forum Mentor

    Location:
    Northampton
    Business Name:
    None
    Sounds like a daft question, but, what mA RATING is the socket
     
  9. dnjr
    Offline

    dnjr Electrician's Arms

    Location:
    South coast
    30mA
    Doesn’t trip on ramp test either
     
  10. westward10
    Online

    westward10 In echoed steps I walk across an empty dream. Staff Member Moderator

    Top Poster Of Month

    Location:
    Northamptonshire
    Take one home and temporarily connect it and retry.
     
    • Agree Agree x 1
  11. dnjr
    Offline

    dnjr Electrician's Arms

    Location:
    South coast
    H
    Evening Westward. Good call. Will do that when I can get back in there
     
  12. Midwest
    Offline

    Midwest Electrician's Arms

    Location:
    Oxfordshire
    Agree with Strima, think you may have an IR fault. Have you done that test? Had similar experiences before, RCD not tripping & RCD tripping on Zs test. Both done to IR fault, neutral earth. That said, that was RCD at origin of circuit, but worth considering.
     
  13. Gavin John Hyde
    Offline

    Gavin John Hyde Electrician's Arms

    Location:
    Somerset
    Business Name:
    Sulis Electrical Services Ltd
    are they passive or active rcd sockets?
    I had an issue testing rcd sockets before now, they were passive ones, simply didnt always trip on a 1 or 5 x test. They were passive ones, they were a new generic unbranded model out at the time and cheap nasty stuff from far east. I took them back for a refund and turns out they later got recalled as the passive circuitry inside was no good.
    I have heard that passive as opposed to active rcd sockets can cause issues with testing as they have the reset part built in.
     
  14. dnjr
    Offline

    dnjr Electrician's Arms

    Location:
    South coast
    These are timeguard active ones. I wondered if they need a ‘special ‘test but apparently not
     
  15. Pete999
    Online

    Pete999 Forum Mentor

    Location:
    Northampton
    Business Name:
    None
    Idn't mean to shout I was on the phone, and doing two things at once confuses me, must be getting old!!
     
    • Like Like x 2
Loading...
Similar Threads - Timeguard socket won’t Forum Date
can you sort the sockets out . Electrical Forum Tuesday at 6:19 PM
Bathroom electrical wiring - fan and shaver sockets Electrical Forum Tuesday at 3:50 PM

Share This Page

Users found this page by searching for:

  1. trip with sicket

Electricians Directory Post a Domestic Job Post a Commercial Job