Dear All
Installation tncs. Wyler re-wireable fuses
I’ve fitted 2 x timeguard rcd sockets to provide protection for extension leads going outside but neither will trip with my tester. Trip fine on test button
Also trip when I do earth loop test ( fluke tester)
Socket tester says it’s all ok
Zs before I changed to rcd socket was 0.45
Doesn’t trip on ramp test
Ze 0.21
What the hell am I missing

Advise appreciated
Cheers
 
Circuit IR results?

Does your test meter trip other RCDs?
 
I've come across faulty SRCDs out of the box before. Obviously without having seen the installation I can't say that this is the case here but certainly it is possible.
 
I've come across faulty SRCDs out of the box before. Obviously without having seen the installation I can't say that this is the case here but certainly it is possible.
Hi Risteard
I thought of faulty rid but to have two , one single socket one double would be very odd. I rang timeguard and they said it was possible so am getting two more from wholesaler but don’t expect it to cure it
To be honest I was expecting someone to rip me a new one and say I’d missed something obvious
 
Agree with Strima, think you may have an IR fault. Have you done that test? Had similar experiences before, RCD not tripping & RCD tripping on Zs test. Both done to IR fault, neutral earth. That said, that was RCD at origin of circuit, but worth considering.
 
are they passive or active rcd sockets?
I had an issue testing rcd sockets before now, they were passive ones, simply didnt always trip on a 1 or 5 x test. They were passive ones, they were a new generic unbranded model out at the time and cheap nasty stuff from far east. I took them back for a refund and turns out they later got recalled as the passive circuitry inside was no good.
I have heard that passive as opposed to active rcd sockets can cause issues with testing as they have the reset part built in.
 
are they passive or active rcd sockets?
I had an issue testing rcd sockets before now, they were passive ones, simply didnt always trip on a 1 or 5 x test. They were passive ones, they were a new generic unbranded model out at the time and cheap nasty stuff from far east. I took them back for a refund and turns out they later got recalled as the passive circuitry inside was no good.
I have heard that passive as opposed to active rcd sockets can cause issues with testing as they have the reset part built in.
These are timeguard active ones. I wondered if they need a ‘special ‘test but apparently not
 
Agree with Strima, think you may have an IR fault. Have you done that test? Had similar experiences before, RCD not tripping & RCD tripping on Zs test. Both done to IR fault, neutral earth. That said, that was RCD at origin of circuit, but worth considering.
Yep. IR test done before I started
L/e 180m. L/e 179m. Limited l/n as I couldn’t get to dishwasher or washing machine sockets
 
Agree with Strima, think you may have an IR fault. Have you done that test? Had similar experiences before, RCD not tripping & RCD tripping on Zs test. Both done to IR fault, neutral earth. That said, that was RCD at origin of circuit, but worth considering.
Yep. IR test done before I started
L/e 180m. L/e 179m. Limited l/n as I couldn’t get to dishwasher or washing machine sockets
 
Dear All
Installation tncs. Wyler re-wireable fuses
I’ve fitted 2 x timeguard rcd sockets to provide protection for extension leads going outside but neither will trip with my tester. Trip fine on test button
Also trip when I do earth loop test ( fluke tester)
Socket tester says it’s all ok
Zs before I changed to rcd socket was 0.45
Doesn’t trip on ramp test
Ze 0.21
What the hell am I missing

Advise appreciated
Cheers
Just been informed I’ve reached 100 posts. Does that mean I can attend the electricians arms. Could murder a pint
 

Reply to Timeguard rcd socket won’t trip with tester. Help please in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K
I have just popped out to a frustrated customer who has had intermittent tripping of a 30mA RCD for years, on average 5 - 10 x p/month. It used to...
Replies
31
Views
4K
Hey everyone help needed please. Moved into a new home, and have just had all the first fit installed for a new kitchen. During first fit, the...
Replies
12
Views
2K
Hi all can anyone give me the logic why the RCD wouldn’t trip on a neutral/earth fault. Testing a extension where they have added in 5...
Replies
42
Views
7K
Q1: I am not far off getting professional in but which professionals and how to find a good one? I have researched and investigated a bit myself...
Replies
14
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock