Search the forum,

Discuss TL inverters and TT earthing systems? in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

R

Ross Harvey

HI

Im after a bit of advise.

Im a suby for british gas wiring heating systems. When a salesman goes to quote a job they have to do a "socket and see" test on a circuit to see if the main earth is sufficient. (not a great way to test it by hay-ho). Anyway this installation fails the test. so they send me in to do a proper inspection. It turns out that it needs the main earth upgrading. In this case we sell them an earth rod pack. This is where it gets interesting. The main cut out fuse for this installation is in a neighbours house (great!).Also he has a Sunnyboy 4000TL already installed. As this is a TL inverter i cant put the whole installation on a 30mA RCD.

So my question is can i put a 100mA RCD in instead?

I know some might say just get them to upgrade there earth through the DNO, but i would rather the work myself (selfish i know, but work is work).

Any advise would be appreciated.

Thanks
 
I'd get the DNO out to sort the Earth out as Marvo said. And I would split the supply so that you got the house on its consumer unit and then install a 2 way consumer unit for the PV. That way you would have a 30ma on each consumer unit. It's recommended to install PV on it's own RCD to avoid nuisance tripping with all the combined Earth leakage of the house and PV
 
The pv circuit is already on its own consumer unit. But not on an rcd. TL inverters are not supposed to be protected by a 30 mA rcd. I new that getting the DNO to re new the earth would be best solution. I was just wondering if I could use a 100mA rcd instead of a 30mA.
 
Is there any reason why the TL inverter needs to be on an RCD? Such as how the array is installed or the route of the AC cable? If not, then what's the issue?

ETA Ah, now that I've read the thread properly, I see what you mean.

Surely getting the DNO out is the right thing to do. If a TNS is achievable then surely it is desirable over a TT setup?
 
Last edited by a moderator:
Yes 100 ma RCD will be fine. You may actually find the Inverter manufacturers instructions state that it should be protected by 100ma RCD protection.
 
Yes 100 ma RCD will be fine. You may actually find the Inverter manufacturers instructions state that it should be protected by 100ma RCD protection.


Don't see how you can say that, one of the issues is DC leakage and thus holding the RCD closed. Sibert will post you the appropriate technical documents from Doepke in Germany if you like.

100mA Type B I'd agree with, have you seen the prices of one of those though :) - Andy at Sibert will sell you one quite happily :)
 
Don't see how you can say that, one of the issues is DC leakage and thus holding the RCD closed. Sibert will post you the appropriate technical documents from Doepke in Germany if you like.

100mA Type B I'd agree with, have you seen the prices of one of those though :) - Andy at Sibert will sell you one quite happily :)

I was aware that as the sunny boys AC/dc inputs are electrically separated there wasn't as issue with reverse dc currents??

High ze is DNOs problem. Call them out to sort the issue IMO :D
 

Reply to TL inverters and TT earthing systems? in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top