My neighbour had problems with her RCD tripping in the main consumer unit and she indicated it may be linked to her fish pond set-up outside the property which is fed from a plug socket in the garage.
We investigated that this particular garage circuit was on a B16. We powered up the breaker but there was no power from the garage. Further investigation led us to find an RCD protected sub-board in the garage.
The feed for the RCD protected sub-board is also RCD protected - is this correct or would it be more practical to move the feed B16 breaker over to the non-RCD side?
The feed exits the house via an IP rated enclosure and two-core SWA is used for the feed to the sub-board. The main earth for the sub-board disappears under a pathway. We can only assume that it is connected to a buried Earthing Rod. Would it have been better to supply the sub-board with Twin & Earth SWA?
We fed the sub-board via a B16 breaker on the non-RCD side (temporary link) so we could obtain a Ze reading, which was 30 ohms (main consumer unit TNC-S Ze = 0.16 ohms).
We know that a TT system should be a maximum of 21 ohms but we are a little unsure of the 200 ohm limit for a TT system stated in the On-Site Guide.
We did a Zs at a garage socket and obtained a reading of 31.2 ohms. Would this be within tolerance?
RCD’s tripped within the acceptable tripping times. How does this affect the readings as it is tripping two RCDs?
The main source of the tripping was because the UV light for the fish pond had blown and my neighbour was unaware that there was a sub-board in the garage, which when found and switched on, power was re-instated to the garage.
Any advice on the above would be a great help as we have never worked or taken readings on a TT/mixed system before.
We investigated that this particular garage circuit was on a B16. We powered up the breaker but there was no power from the garage. Further investigation led us to find an RCD protected sub-board in the garage.
The feed for the RCD protected sub-board is also RCD protected - is this correct or would it be more practical to move the feed B16 breaker over to the non-RCD side?
The feed exits the house via an IP rated enclosure and two-core SWA is used for the feed to the sub-board. The main earth for the sub-board disappears under a pathway. We can only assume that it is connected to a buried Earthing Rod. Would it have been better to supply the sub-board with Twin & Earth SWA?
We fed the sub-board via a B16 breaker on the non-RCD side (temporary link) so we could obtain a Ze reading, which was 30 ohms (main consumer unit TNC-S Ze = 0.16 ohms).
We know that a TT system should be a maximum of 21 ohms but we are a little unsure of the 200 ohm limit for a TT system stated in the On-Site Guide.
We did a Zs at a garage socket and obtained a reading of 31.2 ohms. Would this be within tolerance?
RCD’s tripped within the acceptable tripping times. How does this affect the readings as it is tripping two RCDs?
The main source of the tripping was because the UV light for the fish pond had blown and my neighbour was unaware that there was a sub-board in the garage, which when found and switched on, power was re-instated to the garage.
Any advice on the above would be a great help as we have never worked or taken readings on a TT/mixed system before.