TNS

Discuss TNS in the Commercial Electrical Advice area at ElectriciansForums.net

Reaction score
15
Should I be getting a dead short at DB on ohms scale when connecting leads of ohm meter across neutral bar and earth bar or would that only apply to TNCS??
 
What reading are you getting and with what are you measuring it with.
Meggar 1720 mft...
My "issue" is I'm trying to figure out if I should or should not be getting a dead short.
I have a DB with dual supplies(A+B)

On A supply on ohms scale I am getting a dead short(0.03)ohms
On B supply I am showing open circuit.

They are fed from 2 different substations(both containing H.V transformers)

I'm thinking maybe I shouldn't be getting a short.And I maybe have a neutral earth fault,but due to only having a 3 pole switch I cant isolate the neutral unless I can get access to LV switchboards to remove neutral link on mccb
I was just trying to figure out generally if I should be expecting to see dead short.The cable run is just about 30M.
 
Ok, with TNS I would not expect to see 0.03 Ohms N-E. What size cables? And when you say 30m run - from where to where please?
 
Last edited:
Hi,bud,Could do with less of the dead short,as myself and six of my pals,are feeling the lack of diversity treatment ;)
 
Ok, with TNS I would not expect to see 0.03 Ohms N-E. What size cables? And when you say 30m run - from where to where please?
From DB to HV/LV substation 70mm cable (my understanding of tns is the neutral is derived from the earthed star point on the secondary windings .I'm wondering has the earth been omitted to the neutral.)
 
Assuming 70mm conductor size for both N, at 20C the resistance for 30m is about 0.024Ohms. And a 37m run would be 0.03Ohms. Unless I've made a no-coffee-yet mistake.
 
Last edited:

Reply to TNS in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

Hello. New member here. Electrical enthusiast. I am at a friend's house in the Bahamas and decided to look at the load center in the house, which...
Replies
2
Views
393
Hi was recently at a property and was installing a Solar PV system. was doing my testing and i came across a weird result when doing the...
Replies
23
Views
3K
So I’m an apprentice and I’m just trying to get a better understanding of the science behind this because the electricians who have said it have...
Replies
12
Views
1K
On an EICR I found a 200 amp 3ph supply, TNS earthing (which looks original) and Ze of 19 ohms. No rods. No RCDs. L1 -> N was about 0.5 ohms...
Replies
11
Views
952
I have breaker box at least 40 yrs old, both conduit and romex enter box, only one neutral bar that all white wires and bare ground wires attach...
Replies
4
Views
722

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock