Yes,and?Well a dead short is little or no resistance.
Meggar 1720 mft...What reading are you getting and with what are you measuring it with.
Thanks for your reply but I thought I made that pretty clear in the titleOk, first question is what is the installation means of earthing?
Sorry Peg(or porg in a morgue if you prefer)Hi,bud,Could do with less of the dead short,as myself and six of my pals,are feeling the lack of diversity treatment
Yep good for you. Best wishes.Thanks for your reply but I thought I made that pretty clear in the title
From DB to HV/LV substation 70mm cable (my understanding of tns is the neutral is derived from the earthed star point on the secondary windings .I'm wondering has the earth been omitted to the neutral.)Ok, with TNS I would not expect to see 0.03 Ohms N-E. What size cables? And when you say 30m run - from where to where please?
Theres a fault on a circuit yes.Its a new installation.About to be handed overHi,was there a reported fault,which instigated your testing?
A couple of months ago yes when it was first powered up..As far as I remember it was around 0.07..(quite big job over a hundred DBs so not sure)Have you carried out a Ze at the boards.
No continuity on an accessory fault traced to defective modular kit.faulty circuit disconnected (I think)unless labled wrongly.not confirmed yet.What is the nature,of the fault?