Discuss Tripping issue with Split load Wylex DB in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
24
Got an issue at home, today I got home and found one of the RCD's had tripped on my split load Wylex DB.
I tried to reset but it wasn't having it. Switched all MCB's off on the RCD (Call it number 1) that had tripped then reset. All was ok, switched each MCB on and stayed in.
Put the kettle on (which is on the other RCD (call it number 2) and on the kitchen circuit) and it tripped RCD number 1, kettle carried on boiling without an issue to the RCD 2 or the MCB it is on.

House was rewired in 2016 and the new board installed then

HELP, I am at my wits end which is a very short journey

Any ideas will be greatly received. Give me 3 phase any day of the week
Wylex DB.jpg
 
Best you find a local spark with an MFT, an earth leakage clamp meter and time on his hands

Have you unplugged all items on these circuits?
All items on the circuits on the RCD have been unplugged. But still it trips when anything on the kitchen circuit is switched on. We just tried each appliance in turn and each one tripped the RCD out. Weird the mcb and RCD that protects the kitchen circuits never tripped
 
Best you find a local spark with an MFT, an earth leakage clamp meter and time on his hands

Have you unplugged all items on these circuits?
Council property and all we got was your cooker is causing the issue. The cooker has been completely disconnected from the outlet and still it trips
 
Have it to hand when a spark is investigating - changes in IR readings may be very eye opening..........

BUT have you unplugged everything ? Washing machines? Dish washers? Ovens ?
The cooker was totally disconnected, washing machine dishwasher and tumble drier are on the kitchen circuit on the RCD that's not tripping. Just confused why after 2 years it's going ---- up
 
Have it to hand when a spark is investigating - changes in IR readings may be very eye opening..........

BUT have you unplugged everything ? Washing machines? Dish washers? Ovens ?
The cooker was totally disconnected, washing machine dishwasher and tumble drier are on the kitchen circuit on the RCD that's not tripping. Just confused why after 2 years it's going ---- up
is it still ?
is it still ?
Yes, I am giving up for tonight and will take the day off tomorrow to try and sort it
 
The cooker was totally disconnected, washing machine dishwasher and tumble drier are on the kitchen circuit on the RCD that's not tripping. Just confused why after 2 years it's going ---- up


Yes, I am giving up for tonight and will take the day off tomorrow to try and sort it

Mice? water leak? trapped cable? DIY infliction?

Do you have any proper test kit?
 

Reply to Tripping issue with Split load Wylex DB in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K
Cant get my head round this :( I understand N-E faults cause RCD's to trip, but I cant understand why on these 2 occasions, googled allover but...
Replies
13
Views
1K
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
780
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K
I have just checked a double outlet and it trips at 18ma. It was supposed to be faulty. Washing machine had a bad heater which got replaced but...
Replies
10
Views
567

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock