jenions

recently changed an old fuseboard to a new MK consumer unit with 2rcbo's and then RCD with 5 mcb's on it, now i IR all the circuits and all came out at <299Mohm but since day 1 the rcd has tripped whenever a high load is switched on? i tried the up and down ring and the fridge radial on 1 of the rcbo's (40A) and they worked fine but if i put them back on the rcd side they trip. anybody got any ideas? also the test button on the rcd isnt working, now this is the 2nd rcd ive tried as i changed the 1st 1 just incase that was faulty.
 
Did you test for an earth?

seems like a odd one, one of them " have to be there ones " haha

Good luck, try the above suggestion though
 
seen something similar once before, could be reverse polarity somewhere.

everytime customer used hoover rcd would trip. located mixed connections in thermostat which plumber had connected
 
have several times found where customer has replaced a socket face and has reversed N/E. as soon as a load is applied, the RCD will trip.
 
easier way would be to interconnect live and earth and do r1 + r2 test at board and locate fault like that. you'll soon find where its been connected wrong
 
it may sound obvious but make sure the neutrals for the circuits connected to the RCD are indeed connected to the RCD it sounds as if a neutral is in the wrong place in the CU.
Test button should work if L and N are connected correctly check polarity at the incoming main switch on the CU. If LN ok and test button not working take it back and exchange RCD as faulty.
What type of earthing system is it?
What was the Ze ?
Did you carry out a full PIR and schedule of tests before changing the CU?
 
Did you notice anything strange about those boards?

Like the main switch has to be levered into the off position but flicks on!!

I had a similar problem last night, it was the fish pond pump.
 
no rcd before hand jus old wylex fuse board, got a borrowed neutral but sorted that at the moment by putting them in same rcbo till i can run a new cable. i tried numerous high loads such as tv, fridge, 3kw heater even me sds drill but all tripped it. i got a low ze cant remember reading i wrote it down and its with all me gear on a job, its just thrown me as this is the second rcd ive tried which makes me think its something on the installation.
 
When you carried out IR test I assume all loads were disconnected. It seems that there may be a leakage problems on the loads rather than fixed wiring, the old CU would not detect earth leakage on loads. PAT testing of the appliances that trip the RCD might help. If you cannot isolate one load as the cause it may be a cumulative effect IE 15mA leakage on more than one load.
 

Reply to trouble with newly installed MK c/u in the Australia area at ElectriciansForums.net

Similar Threads

I had a call to a new customer who was experiencing what sounded like nuisance tripping on a kitchen ring. Some background first. It's an MK LN...
Replies
4
Views
686
Doing one more of the flood of EICR today on a rented property before a tenant change, but ran into a slightly interesting case so would...
Replies
71
Views
12K
Hi guys I have this problem that I've been trying to figure out all week. On friday I had a 5 tail economy 7 smart meter installed and every...
Replies
30
Views
7K
Hi Don’t often post on here but I’ve dreamt about this issue last night. Need advice please Yesterday I attended a property to complete an EICR...
Replies
9
Views
1K
Toneyz
T
Hi all, Any help would by greatly appreciated as i have tried everything i possibly can. Heres some info on the situation, installed some spike...
Replies
18
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock