Just noticed that the requirement for RCD protection has been removed for TT installations.
Discuss TT and RCD protection in the UK Electrical Forum area at ElectriciansForums.net
The 17th did that. RCD protection has not been mandatory for a TT system since the 16th Edition.Just noticed that the requirement for RCD protection has been removed for TT installations.
Precisely. It's a decade new.I'm pretty sure that reg you have given was in the 17th, so nothing new.
Once got an RA of 6 ohms on a steel farm building by drilling and tapping a girder for the lug.Would have been ok for a B6 on a lighting cct I think.Essex, you're always (or rather 99.9% of the time) going to need an RCD for TT as you'll never be able to meet the Zs values unless the Ra<1Ω which (unless you are Trev) is nigh impossible.
I'm pretty sure that reg you have given was in the 17th, so nothing new. Would be very interesting to know if anyone on here has ever been able to get an Ra low enough to forgo an RCD on a TT though?
Essex, you're always (or rather 99.9% of the time) going to need an RCD for TT as you'll never be able to meet the Zs values unless the Ra<1Ω which (unless you are Trev) is nigh impossible.
I'm pretty sure that reg you have given was in the 17th, so nothing new. Would be very interesting to know if anyone on here has ever been able to get an Ra low enough to forgo an RCD on a TT though?
I would bed to differ. The last TT system we tested was 0.73 and that was only a single rod.
Although I do agree it is unlikely to be ever able to prove a permanently and reliable Zs on a TT system it does loosen the requirements a little and in this case a 500mA RCD would be more than enough.
Had one the other week and it's been bone dry for a while...Think the installer may have hit an earthed source . Done loads of TT systems, to get an RA of 0.73 ohms with one electrode I’d need to see it to belive it and then see it again
Next to no chance that is off one rod though, unless they have nicked something on the way down
That's what I’m thinking.Next to no chance that is off one rod though, unless they have nicked something on the way down
Reply to TT and RCD protection in the UK Electrical Forum area at ElectriciansForums.net