Discuss TT and RCD protection in the UK Electrical Forum area at ElectriciansForums.net

Essex, you're always (or rather 99.9% of the time) going to need an RCD for TT as you'll never be able to meet the Zs values unless the Ra<1Ω which (unless you are Trev) is nigh impossible.

I'm pretty sure that reg you have given was in the 17th, so nothing new. Would be very interesting to know if anyone on here has ever been able to get an Ra low enough to forgo an RCD on a TT though?

Are you talking domestic?
I've worked in industrial units, multi rodded, maybe nested with Ra of well under. You'd think they were TN, until closer examination.
 
Last week on a new install we put 5 rods down into what seemed like sand to achieve an Ra of 132.4 ohms. We only stopped at 5 because we ran out of rods. This week we will be digging a new trench from the incoming supply building to an area of much firmer ground so that another rod will provide a more acceptable result.
Incidentally, 400v supply leaves the meter and hits a distributors 4 pole switch, then a 4 pole 100mA/100A Time delayed RCD. Splits 3 ways to 2x 3P+N switch fuses for distribution to remote buildings and a local 1P consumer unit for construction supply, treatment plant & local lighting.
 
I would bed to differ. The last TT system we tested was 0.73 and that was only a single rod.

Although I do agree it is unlikely to be ever able to prove a permanently and reliable Zs on a TT system it does loosen the requirements a little and in this case a 500mA RCD would be more than enough.

must be all that fake tan lotion soaked into the ground.
 
Quick question guys im moving my board 5 metres. Currently on a tt system but within the next few months will have western power convert it to tncs. But in the mean time would it be ok to put up just a kmf switch or a time delayed rcd before the tails?
 
all depends on whether the new tails require RCD protection.
 
so they are not buried in wall/s <50mm deep, so RCD protection is not required. just fit a KMF, fused accordingly ( i.e. if DNO fuse is 100A KMF fuse should be 60A or 80A.)
 

Reply to TT and RCD protection in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi everyone, I have been asked to pull in some new 3 phase supplies for 7 new welders which do not require a neutral connection. The client has...
Replies
4
Views
686
hi all come across a new build commercial office where radial circuits feeding electrak power track was protected by 32A RCBO at dist board and...
Replies
15
Views
971
Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
721
Hello! I've been racking my brain this evening about some RCD selections. I've been doing some work for a solar installer, and they've asked me...
Replies
5
Views
891

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock