Discuss TT and RCD Protection in the UK Electrical Forum area at ElectriciansForums.net

T

thomas-1981

I was doing work on an commercial site today. The supply is TT and the install is about 25 years old. I was under the impression a TT system had to be RCD protected to meet disconnection times. But this install only had a few circuits with RCBO's. Would the version of regs the install was designed to not require RCD protection? Thanks
 
around that time it was usual to fit an up front 100mA RCD on a TT system. if you are doing any work in it, i'd be inclined to fit a new CU with 100mA delay RCD as main switch and 30mA RCD/RCBOs for all circuits.
 
I was doing work on an commercial site today. The supply is TT and the install is about 25 years old. I was under the impression a TT system had to be RCD protected to meet disconnection times. But this install only had a few circuits with RCBO's. Would the version of regs the install was designed to not require RCD protection? Thanks

If it had RCBO,s this would give you your RCD protection would it not ?, unless you meant MCBs ?
 
"Shall we eat grandma?"
"Shall we eat, grandma?"

Big difference. ;)

One day... One day, I will have summat useful to contribute other than inanities.
 
I was doing work on an commercial site today. The supply is TT and the install is about 25 years old. I was under the impression a TT system had to be RCD protected to meet disconnection times. But this install only had a few circuits with RCBO's. Would the version of regs the install was designed to not require RCD protection? Thanks

What was the Ra?
 

Reply to TT and RCD Protection in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi there , Currently doing a college project where i need to select protective devices for the contract. I'm now at the point of selecting SPDs...
Replies
5
Views
2K
Afternoon everyone, I have a quick question about the Tesla Gen 3 Wall Charger? Does it require Type A 30MA RCD protection or not. Only because...
Replies
3
Views
1K
The earthing arrangement where the hot tub will be installed is formed in the TN-C-S system. I want to install the sub-main distribution circuit...
Replies
18
Views
2K
I'm doing a college design project and need to choose a suitable range of circuit protective devices for the whole contact. I've chosen and...
Replies
7
Views
3K
On a TT system the rcd must operate withing 0.2 seconds for many circuits. Why when we test rcd's does it not say 300ms for TN systems or 200 ms...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock