Hi, a bit of advice required. I need to install another d.b to a garage, the tails are to be split. The earthing system is TT, the cable is armoured, clipped to the side of the building & over to the garage on a small cantenary wire. As it is TT would the distribution cable need to have rcd protection? I have been told it doesn't, but the regs stipulate 1 second disconnection time.

Cheers
 
bit you'll need the RCD for fault protection to achieve your disconnection time.
 
I would put a 100ma type s (time delayed) then your switched fuse to protect your distribution circuit. Then 30ma RCDs to cover circuits from 2nd DB.
 
Thanks for advice, much appreciated,

I was going to use a 100ma as the cable was clipped, i would have used 30ma if cable was buried.

why use 30mA for buried cable - mole protection?
 
Thanks for advice, much appreciated,

I was going to use a 100ma as the cable was clipped, i would have used 30ma if cable was buried.
you are using an SWA...so this cable type enjoyes an earthed metallic covering yes...

so no need for the 30mA for it...and dont forget as well if you gave the SWA 30mA top end for fault protection...then how are you going to split the finals and acheave discrimination & diversity?..

got to think these things through mate ....
 
I always thought 30ma had to be used when buried on TT, incase someone cut through the cable. Thanks for that appreciated.

no. the 30mA RCD is for all final circuits, not distribution circuits. it's the fault protection that protects SWA form damage. in this case an RCD is used on TT systems as the EFLI is too high to achieve disconnection times, generally 5 secs. for a dist. cct.
 
no. the 30mA RCD is for all final circuits, not distribution circuits. it's the fault protection that protects SWA form damage. in this case an RCD is used on TT systems as the EFLI is too high to achieve disconnection times, generally 5 secs. for a dist. cct.
and finals over 32A...which begs me to ask after looking at a recent condition report carried out by a so called `competant person`...he had put 63A OPDs down as .4
as well as a multitude of other made up crap..

well i guess you sees stuff every day....
 
no. the 30mA RCD is for all final circuits, not distribution circuits. it's the fault protection that protects SWA form damage. in this case an RCD is used on TT systems as the EFLI is too high to achieve disconnection times, generally 5 secs. for a dist. cct.

That's really helpful.

Cheers
 
Hi, a bit of advice required. I need to install another d.b to a garage, the tails are to be split. The earthing system is TT, the cable is armoured, clipped to the side of the building & over to the garage on a small cantenary wire. As it is TT would the distribution cable need to have rcd protection? I have been told it doesn't, but the regs stipulate 1 second disconnection time.

Cheers
depending on over current protection i think you find it 0.2 sec
 
distribution circuit, 1 sec. (see 411.3.2.4.) it's 0.2 secs. for finals.
 

Reply to TT distribution circuit in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K
I'm doing a college design project and need to choose a suitable range of circuit protective devices for the whole contact. I've chosen and...
Replies
7
Views
3K
For context i am in my 2nd year in college and my head is going round in circles a question in my project for which i need to select the right...
Replies
22
Views
4K
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K
The earthing arrangement where the hot tub will be installed is formed in the TN-C-S system. I want to install the sub-main distribution circuit...
Replies
18
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock