Andy C

-
Reaction score
19
I have a replacement consumer unit coming upon which is currently off a TT system with a nice low reading on the earth. There is no chance of the DNO converting to TNCS. No SPD or AFDD as per client.

I intend fitting a new Dual RCD consumer unit.

I have researched this site and there was talk of the main switch being swapped out for a 100mA time delayed RCD. Albeit as I understand all this will protect is the internal wiring from the main switch to the RCDs. The use of the glands and cleating of mains tails would reduce the chance of any damage.

1/ I am led to believe that a dual RCD board would not protect all the circuits.

2/ I believe that a dual RCD would be permissible and would not lose any protection even if one RCD was to trip.

My questions are which is correct 1 or 2, i believe its 1, secondly would you still replace the main switch with a time delayed RCD.

Thanks in advance.
 
Hi - provided there are no “high integrity” circuits connected prior to the RCDs then no need for 100mA time delay RCD upfront, in my view. Glands and clamps yes by all means.
 
Guys I have sorted this now. The internal wiring on consumer units between main switch and RCDs is fine as long as the manufacturers cables are used. You also have to ensure the mains tails are in a gland and are cleated which I do anyway.
 

Reply to TT earth, Dual RCD or RCBO and Main Switch in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Need some advice, I have 7 static caravans to connect which need to be connected via TT 1. All the vans have a 30ma RCD main switch internally...
Replies
6
Views
855
I'm in a questions asking mood tonight. I briefely looked at a job today and I need to recommend a board change but need to justify it. Firstly...
Replies
7
Views
1K
The earthing arrangement where the hot tub will be installed is formed in the TN-C-S system. I want to install the sub-main distribution circuit...
Replies
18
Views
2K
Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
717

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock