Evening men!

Looked at a upcoming rewire
it is for a mid terrace old house.

A single phase comes into the house next door- one 60a head in next doors house >>meter>>cu
Then a 2nd feed goes into the house I am planning to rewire into a 60a head>>meter>>cu

I have seen this before- but what concerns me is the earthing
it is just a bonding clamp around the incoming servive- then into a met in each house
so a TNS

however upton getting a quick ze reading it was 4.3ohms- likely to be loose clamp

The builder got UKPN out and they said this to him:

"Single supply to no17 with a link to no 15 through the wall as we knew.

When Installed by London Electricity Board 50 or so years ago no earth was provided. UKPN having adopted the network will not and do not provide an earth where it is not present such as on a TT supply like this one.

The earth next door is not fitted or owned by UKPN (nor is the link between 15 and 17 oddly but they do own the head in 15...) If the steel pipe that covers the lead insulation of the supply underneath is in good contact and the pipe is very clean of rust under the earth bonding it could be a good earth. If its not it wont be.

2 options.

1- New Supply - PME.

2 - Earth Spike"

the client can not afford a new PME supply

If I go down the route of install a rod and making it a 'offical' TT system do I need a upfront RCD

they want the c/u remote from the meter so it will go meter >> sw isolator>> cu via 3c SWA
the consumer unit will be dual 30ma rcd

do I need a upfront 100ma rcd to cover the SWA sub main or am I over thinking again!
 
Don't forget you'll need to take precautions bringing tails into that enclosure with a likely high Ra. Unless of course you are a certain engineer who used to be on here who always got sub 1 ohm Ra's
 
would you guys feel inclined to leave the 16mm connected to the clamp around the incoming next door- as this is giving me 4.3ohms as well as the rods

would struggle to get that with a few rods??
 
So put a temp board in for this job this morning.
2meter of rod into ground with 16mm earth into MET
100ma time delaying RCD+ fuse carried combo (used PROTEK as wholesaler stocked it)

into a temp board

I got a live Ze reading (test meth 2) as I do not have a electrode tester

The reading was supprising 3.05ohms (I was expecting alot higher for 2m rod!?)

but it did go down pretty easy so guessing the ground was nice and soft

1)on my easycert form what is the 'resistance to earth' reading?
2) what is the 'rated time delay in ms' value- doesnt say on the protek rcd which is model 'T80-100-2TD'
 
Hi - that is very good and that's your number.
For rated time delay - it depends on which standard the RCD was made to. If you've got your OSG the info is in chapter 11, p112.
 

Reply to TT earthing on a rewire in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Evening everyone . Currently looking at pricing a job up . It’s a hot tub supply . Outside socket with a few spare ways in an outdoor cu . 10mm...
Replies
7
Views
494
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Ukpn have put a supply in for us to feed an outside cabinet, which will eventually supply foul water, sewage pump's. They have supplied an earth...
Replies
12
Views
2K
Hi do tt earth systems highly require a rcd, and if not are upfront rcds a must in the tt earthing systems? Cheers
Replies
27
Views
3K
Carrying out a EICR in a commercial setting. In the main intake room the DNO supply comes in and it states clearly this is a PME system. 5 years...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock