Hi all, hoping someone can help. Have a car park with its own supply, meter box located in the corner of a shared car park, TT system. Small db located inside meter box supplying only two circuits, one for car park lighting and one for electric gates. My question is does this installation require at least a 100ma rcd due to it being a tt system. Only current protection for the circuits are 60898 MCB'S. All electric connections and meter box are only accessible via key / tool and there are no user controls.
 
Hi all, hoping someone can help. Have a car park with its own supply, meter box located in the corner of a shared car park, TT system. Small db located inside meter box supplying only two circuits, one for car park lighting and one for electric gates. My question is does this installation require at least a 100ma rcd due to it being a tt system. Only current protection for the circuits are 60898 MCB'S. All electric connections and meter box are only accessible via key / tool and there are no user controls.
whats the Ra you've measured?
 
Thanks. I understand it requires rcd protection to achieve zs but I didn't know if different rules apply as it's not located or serving a dwelling, I regeneration years ago a reg referring to Street lighting
 
What is the Ra?
Presumably pretty low so it might be possible to get it lower and negate the need for an RCD.

Hi


I wouldn't of thought that strategy would be feasible Dave, several points, its not just Ra, Rb also needs to be considered, also who's going to monitor the earthing system what if seasonal variation increases to the point where devices do not operate effectively?

Cheers
 
Last edited by a moderator:

Reply to Tt rcd protection in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
679
Hi guys, could someone help with the following please? The scenario is: Domestic property supplied via three phase (with a 3P main DB, NO SPD)...
Replies
2
Views
465
Keeping this brief.....................New dwelling.....TT system with 100mA S type rcd protected supply to local board with 30mA RCD. Freelance...
Replies
21
Views
3K
Hi Guys, Long time member and not a regular user here. I do pop in here when the odd unknown pop's up and unable to locate an electrical dilemma...
Replies
4
Views
835

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock