sparkyphil1

hi am i right in thinking on a board change for a tt system that the main 60a rccb can be done away with if installing a new plastic ccu with rcbos on all circuits?
existing board is old brown wylex rewireable , no more room on board to facilitate new 10 kw shower circuit.thus board change req

thanks for your replys
 
I would say yes if the tails are short and as you say plastic CU. But with the state of my memory I would get a third opinion.
 
As KFH says, all acceptable, Good Dbl insulated tails, insulated consumer unit, and rcbo's on all circuits, earth loop impedance satisfactory etc.
 
Always prudent to install an up front 100mA S type RCD (or even to replace main isolation switch in CU), on TT installations, as a means of back-up to any downstream 30mA RCD/RCBO's failing...
 
what he said ^^^^^^. that with RCBOs makes the job as good as it can be.
 

Reply to tt system board change in the Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock