Discuss Twin&earth and SWA installed loose on floor in the Electrical Forum area at ElectriciansForums.net
So much for using armoured cable for the outdoor cable run then!
So the SWA is not earthed.The CU end of the SWA has been glanded - but with a stuffing gland:
Now I've received the pictures, I cannot identify what the 'allegedly SWA' cable really is - can anyone identify it from the image below?
So the SWA is not earthed.
Sorry Midwest never used or seen it as far as I know.What if it is NYY-J cable.
We've now firmly established that the conductors are 2.5 sqmm. The spec is not embossed on the cable jacket where we'd expect to find it, but each of the 7 strands of copper in each of the 3 cores is around 0.7 mm in diameter, so πr² X 7 gives us 2.5 sqmm
The spec is not embossed on the cable jacket where we'd expect to find it
Just been looking at this thread again, and have to ask why would your Brother stipulate SWA?The job hasn't been signed off or certified yet. Anyway, I'm advising that my brother shouldn't accept this work.
The contractor was going to do the external run in T&E until my brother (a civil engineer by profession) insisted that SWA be used.
Just been looking at this thread again, and have to ask why would your Brother stipulate SWA?The job hasn't been signed off or certified yet. Anyway, I'm advising that my brother shouldn't accept this work.
The contractor was going to do the external run in T&E until my brother (a civil engineer by profession) insisted that SWA be used.
Civil Engineer=groundworker they are used to installing SWA for the electrical contractor so I suppose he knows it by default as outdoor cable.Just been looking at this thread again, and have to ask why would your Brother stipulate SWA?
Civil Engineer=groundworker they are used to installing SWA for the electrical contractor so I suppose he knows it by default as outdoor cable.
and i got a "bad spelling" for that by a member who's posted less than 30 times in 8 years. hmmm.looks like SWA as Andy says, with the bedding exposed, going to the isolator,and some stripped out inner from isolator to CCU. whatever it is, it's a complete abortion and needs ripping out.
Consider it a badge of honour. They should bring back Teletext.been called some names in the past, but never Teletext. finger hovering over the "dumb" button.
Reply to Twin&earth and SWA installed loose on floor in the Electrical Forum area at ElectriciansForums.net
We get it, advertisements are annoying!
Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.