• IMPORTANT: Please note that nobody on this forum should be seeking from or providing advice to those who are not competent and / or trained and qualified in their field (local laws permitting). There is a discussion thread on this global industry-wide matter HERE. This also has more information about the warning with regards to sharing electrical advice in some countries. By using this forum you do so in agreement to this.

Discuss Two cables connected to mcb in the Electrical Forum area at ElectriciansForums.net

Welcome to ElectriciansForums.net - The American Electrical Advice Forum
Head straight to the main forums to chat by click here:   American Electrical Advice Forum

Jay89

-
Arms
Reaction score
46
Evening All

Im sure this will have been discussed at some point (if so please point me to a relevant thread)

I have been to look at some remedial work where a previous inspector has flagged up on multiple circuits 'DBx Cx has two cables in mcb, need separating - C2'

These circuits are either lighting or radial power circuits supplying a small amount of sockets. All suitably rated and with decent R1+R2 readings.

I have never seen this to be worthy of a mention let alone a C2 code, i have spoken to my CPS technical and they said they cant see an issue. Just looking for anyone else's opinion

Thanks in advance!
 
Your EICR chaps, I don't know. What about RFC's, you got two cables in a mcb there :)
I think they're suggesting two radials rather than two cables is the issue, badly worded title. But yes the specific example they give in the OSG of taking a spur off RFC at the MCB came to mind when i saw it too.
 
I would C3 it, two final circuits require individual circuit protection.

It's not two final circuits, it is one, the definition of a circuit in bs7671 is very clear on this.

What basis do you have for a C3? What is the improvement that can be made? Unless this Mcb is overloaded, which is a separate matter, then nothing is improved by splitting it in to two circuits
 
I suspect this is the case of an existing circuit and then someone lashing another to it because they cannot be be bothered to employ correct installation methods by using an additional protective device at a spare way or advising the existing board has inadequate capacity.
 
I suspect this is the case of an existing circuit and then someone lashing another to it because they cannot be be bothered to employ correct installation methods by using an additional protective device at a spare way or advising the existing board has inadequate capacity.
There are multiple consumer units in this EICR where it has been flagged, from what i can see most seem to be part of original installation (same cable and paired dressing). Mostly on three phase boards with no spare ways.
 